28mm gas pipe ugrade required for 35kw boiler ?

Discussion in 'Plumbing and Central Heating' started by gavm, 4 May 2010.

  1. gavm

    Joined:
    4 May 2010
    Messages:
    2
    Thanks Received:
    0
    Location:
    Devon
    Country:
    United Kingdom
    Hi i recently bought a broag remeha avanta 35c bolier and have just had a plumber round for a quote to install ..

    He has advised i get a bigger gas supply pipe of 28mm from the meter to the boiler cupboard which i currently have 22mm pipework... The meter is approximately 10m from from where the current boiler is situated... Obviously this is going to involve more labour and materials with ripping up the floor etc to make good the upgrade..

    He says i neeed a bigger supply because the boiler is a 35kw and also because im running a gas hob with single gas oven too...

    Can someone please confirm this to be true or is the 22mm pipework i already have adequate to do the job as i had another quote from a heating engineer and he did not mention the pipe upgrade needing to be done...


    Thanks in advance Gavin
     
  2. keighern

    Joined:
    8 Jun 2009
    Messages:
    66
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    depends on number of factures. Needs correct pipe sizing calculations doing to ensure sufficient flow of gas to appliances. To answer your question all installs are different so no definitive answer unless viewed and calculated.
     
  3. greemyamochop

    Joined:
    1 May 2010
    Messages:
    207
    Thanks Received:
    22
    Location:
    Powys
    Country:
    United Kingdom
    Maybe that the second engineer is not as good as your first but either way the only way to be sure is by doing correct calculations with the consumption required for all appliances.

    When its worked out properly it may mean that only some of the pipework needs to be altered but i would say there is a decent possiblity it needs upgrading.

    Mention it to the second engineer, if hes a decent installer hell do the calculations for you, i would if it meant getting the job!!
     
  4. newgas

    Joined:
    12 Oct 2007
    Messages:
    6,236
    Thanks Received:
    369
    Location:
    Lancashire
    Country:
    United Kingdom
    22mm at 10 mtrs with a hob and gas oven on might be OK but in winter say when the demand is high for heating and you are using both hob and oven with the heating on then the gas pressure is reduced to all appliances because it might not be sufficient for max usage.

    That is what you have to work out the MAX usage of appliances and the the size / length of pipe will tell you what the pressure loss will be.

    Undersized pipework can cause problems in your appliances and they can potentially become dangerous.

    Your plumber could just put in a couple of lengths of 28mm from the meter to the 22mm and that should be OK but I'm going with what youve said, but then I'm not there. :rolleyes:
     
  5. mickyg

    Joined:
    24 Aug 2005
    Messages:
    15,990
    Thanks Received:
    3,316
    Location:
    Hertfordshire
    Country:
    United Kingdom
    • Thanks Thanks x 1
  6. gavm

    Joined:
    4 May 2010
    Messages:
    2
    Thanks Received:
    0
    Location:
    Devon
    Country:
    United Kingdom
    Thanks very much guys for all your input..

    After reading your comments i am leaning towards the 28mm having to be used now.

    Cheers Gavin
     
  7. newgas

    Joined:
    12 Oct 2007
    Messages:
    6,236
    Thanks Received:
    369
    Location:
    Lancashire
    Country:
    United Kingdom
    Good choice mate. ;)
     
  8. Boilerman2

    Joined:
    10 Jun 2009
    Messages:
    5,195
    Thanks Received:
    1,001
    Location:
    Suffolk
    Country:
    United Kingdom
    unless the boiler is VERY close to the gas meter a 28mm supply will nearly always be required IMHO ;)
     
  9. Happyplumber

    Joined:
    9 Feb 2009
    Messages:
    3,058
    Thanks Received:
    725
    Location:
    Berkshire
    Country:
    United Kingdom
    pipe sizeing is critical to any band A boiler so its good idea to do a proper calculation and make sure its the correct size


    A big one will be better then a small one :D :D
     
  10. Boilerman2

    Joined:
    10 Jun 2009
    Messages:
    5,195
    Thanks Received:
    1,001
    Location:
    Suffolk
    Country:
    United Kingdom
    Thats what my missus says :confused:
    signed Little John
     
  11. dreadnoughtheating

    Joined:
    31 May 2009
    Messages:
    2,221
    Thanks Received:
    353
    Location:
    Norfolk
    Country:
    United Kingdom
    And yet again (I say this to the regular CC guys answering this thread - you know who we are...) we have the customer supplying the appliance, and querying the technical knowledge of his installer..... should we as GasSafe installers presumably with a living to make, be answering any such queries?

    Answer on a ping-pong ball please

    DH
     
  12. ianniann

    Joined:
    22 Mar 2009
    Messages:
    535
    Thanks Received:
    74
    Location:
    Manchester
    Country:
    United Kingdom
    No way! Meet in secret under a full moon, ban those NVQs that any fool can study for, and only let the first born son of seven generations of gas fitters apply to Gas Safe ;)
     
  13. simond

    Joined:
    26 Oct 2004
    Messages:
    4,163
    Thanks Received:
    290
    Location:
    Surrey
    Country:
    United Kingdom
    I don't think there is a problem with helping people with a question, whether it is gas related or not.

    However I would question the wisdom of the OP buying the boiler and then trying to get someone to fit it.

    Very few dedicated installers (eg: individuals/companies who specialize in boiler fitting) will entertain fitting a customer supplied boiler. I get calls regularly from people who are getting quite desparate having bought a boiler on the internet and can't find anyone prepared to fit it.

    If you want to buy your own boiler I suggest you find an installer first - this might restrict you to a very small number of Gas Safe Registered contractors indeed. Certainly would take me out of the picture.
     
  14. johnjohnscg

    Joined:
    3 Jun 2011
    Messages:
    8
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    What should happen when a gassafe installer hasn't done the calcs as requested for a new install, then the customer's done their own and found the pipe to be undersized after installatio . Who's out of pocket for the upgrade pipe materials?
     
  15. picasso

    Joined:
    8 Apr 2008
    Messages:
    6,106
    Thanks Received:
    1,325
    Location:
    Essex
    Country:
    United Kingdom
    the installer will end up out of pocket, its the installers responability to ensure its done properly,you cannot blame the customer for not doing your job the way it should be done.
     
    • Thanks Thanks x 1