6mm vs 10mm cable for electric shower

Discussion in 'Plumbing and Central Heating' started by gst300, 16 Mar 2011.

  1. gst300

    Joined:
    28 Mar 2009
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    I am replacing a 9kw electric shower with a 10.8kw - or I was until I was told I need to replace the existing 6mm cable with 10mm cable. Is this necessary? What are the consequences if I don't? If it is necessary then it is beyond my capabilities so should I then pay someone to do it or buy another 9kw shower?

    All advise greatly appreciated

    PS: I am a single mum on a tight budget so the cheapest solution is the best one for me
     
  2. onlyfitidealboilers

    Joined:
    11 Jan 2010
    Messages:
    2,022
    Thanks Received:
    151
    Location:
    Aberdeen
    Country:
    United Kingdom
    the shower could draw a lot of electric and the cable may
    burn out due to lenth of run etc will req 10mm tho
     
    • Thanks Thanks x 1
  3. seco services

    Joined:
    3 Dec 2007
    Messages:
    15,642
    Thanks Received:
    1,247
    Location:
    Essex
    Country:
    United Kingdom
    is it in my eyes the safest solution is the best one.
     
  4. 1john

    Joined:
    3 Oct 2009
    Messages:
    3,351
    Thanks Received:
    341
    Location:
    West Glamorgan
    Country:
    United Kingdom
    The 10,8kw shower wont work on the circuit as it is, if it's constucted safely. It will blow the fuse every time you switch it on. You need to replace like for like if you want to keep the job price to a minimum.

    Seco services comment is very very true. You need a safe competent job by a tradesman who will test this work is electrically safe. Not a cheap job. Pop in the electricial forum and read the 'so sad' thread :(
     
    • Thanks Thanks x 1
  5. gst300

    Joined:
    28 Mar 2009
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks guys. I suppos that's pretty much what I expected to hear :(. Think my cheapest option is to buy another 9kw shower, and avoid the rewiring bit.

    Thanks again for the advice
     
  6. JohnD

    Joined:
    15 Nov 2005
    Messages:
    38,343
    Thanks Received:
    1,533
    Location:
    Hampshire
    Country:
    United Kingdom
    You haven't got a combi boiler have you? if you have a cylinder, where is it, and the cold tank (distance and height) in relation to the shower?
     
  7. gst300

    Joined:
    28 Mar 2009
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    No combi boiler. Cold tank in loft - above shower about 6-7metres away. Have had no probs since I moved in (4 years ish) until 2 months ago when shower stopped working and is leaking water. Have now been given a brand new 10.8kw shower - same make, so minimal fuss regarding installation (or so I thought!)

    What am I losing by buying a smaller (and cheaper) 7 or 8 kw shower?
     
  8. JohnD

    Joined:
    15 Nov 2005
    Messages:
    38,343
    Thanks Received:
    1,533
    Location:
    Hampshire
    Country:
    United Kingdom
    less hot water from a less powerful shower (or the same amount of water but not as hot)

    electric showers are quite weedy, especially in winter when the incoming water is colder.
     
  9. ajrobb

    Joined:
    23 Jan 2010
    Messages:
    1,656
    Thanks Received:
    162
    Location:
    Sussex
    Country:
    United Kingdom
    I suggest you check the rating of the fuse or circuit breaker for the shower in your consumer unit (fuse box).
    Assuming winter water temperature of 5°C and shower temperature of 38°C:
    32 A = 7.6 kW (3.4 litre/min)
    40 A = 9.6 kW (4.2 litre/min)
    45 A = 10.8 kW (4.8 litre/min)
     
  10. gst300

    Joined:
    28 Mar 2009
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for that. Think I will get new 9kw - can live with weedy I suppose, but maybe not weedier :)
     
  11. 1john

    Joined:
    3 Oct 2009
    Messages:
    3,351
    Thanks Received:
    341
    Location:
    West Glamorgan
    Country:
    United Kingdom
    The pressure releive valve may have gone on the shower and you may be able to get a replacment from the shower doctor website which will be cheaper than buying a new shower.
     
  12. PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    18,939
    Thanks Received:
    1,991
    Location:
    Londonderry
    Country:
    United Kingdom
    This will depend on the length of run to calculate voltage drop and the method it is installed.
    6mm Twin and earth can carry 47A if clipped direct (ref method C)
    if the the length of the run is less than 33.5 Metres, the voltaged dropped is within the permitted range.
    10.8Kw/230V
    =46.96A
    It's borderline but you don't need to upgrade your cable, providing it's clipped direct, no thermal insulation, run is less than 33.5M
     
  13. simond

    Joined:
    26 Oct 2004
    Messages:
    4,214
    Thanks Received:
    299
    Location:
    Surrey
    Country:
    United Kingdom
    But the 10.8Kw shower should be fused/protected at 50A.

    And then the protection is beyond the current capacity of the cable, and that is without any external factors applied.

    I agree it is borderline, but in the wrong direction. Strictly speaking, the job can''t be done.
     
  14. PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    18,939
    Thanks Received:
    1,991
    Location:
    Londonderry
    Country:
    United Kingdom
    Again borderline but by putting a 45A protective device on the circuit, it would be possible.
    I don't think the overload that will be applied for the period of a shower would be too, disruptive.
     
  15. PEDANTICVINDICTIVEMAN

    Joined:
    10 Jul 2004
    Messages:
    7,283
    Thanks Received:
    1,297
    Country:
    United Kingdom
    I "once" ran a 6mm cable 21 meters, which I was told by an electrician who worked it out on his calculator was the max for an 8.5Kw shower and ok, never again, the cable got shiny and rather hot after 20 minutes of use :cry:
     