ACL Lifestyle mid position valve

Joined
6 Jan 2010
Messages
6
Reaction score
0
Country
United Kingdom
I have browsed the posts regarding failure of the above valve and I think it's a faulty PCB, what are your thoughts please.

Problem: I can get hot water fine but no central heating.
The thermostat is working O.K.

With hot water selected on control unit - If I override (with the knurled button at the end) I can get the WMH lever to manual and lock it in place - result heating.

With heating selected on control unit - If I override (with the knurled button at the end) I can get the boiler to fire up and the pump running but it won't lock in place so it drops back to either W or M (if locked). Locked in position M with just heating selected - nothing!!

Presumably the microswitch is O.K. as it fires up.
 
Sponsored Links
Presumably the microswitch is O.K. as it fires up.
The micro-switches only have any effect when you want CH and HW at the same time or just CH on its own.

The valve does nothing when you have HW on by itself.

How comfortable are you playing with electrics, e.g connecting and disconnecting wires (not live ;))?
 
Thanks for the reply.

No problem regarding wires, live or otherwise.

Today it's started working again !!

Yesterday I tried to 'free' the valve by overriding it several times with the button, I'm guessing this is the reason it's working again.

The WMH is pointing to Heating now.

One thing I have noticed is the system seems quieter than it did before :confused:
 
Sponsored Links
Hope "D_Hailsham" sees this post as he appeared to have some avenues to explore.

I am still without heating unless I over ride the WMH switch to manual and put the water on !!

Any help would be appreciated.

Ian
 
You appear to get CH along with HW, but as soon as HW is satisfied, the valve is supposed to move to CH only position. Your valve is either not moving beyond mid position, or if it is then it does not light the boiler.
In CH only mode, power to light boiler comes from valves orange wire.
In HW mode or HW/CH mode the power is supplied through the cylinder stat.
Of course it could be the valve is stiff, so it would be better to first remove the head off the spindle and test spindle. Should be able to turn it with finger and thumb.
The motor has to work against the resistance of the valve and the return spring.
Other than that, the actuator head is likely to have faulty micro switches with dirty/burnt contacts, so replacing the head is next best option.
This assumes of course that there is no problem with wiring.
 
Thanks for the reply Mandate, I will take a look at the weekend and see if that helps - Cheers
 
Thanks for your help, I've checked all the wiring and micro switches and everything was fine, it turned out to be a dead motor.

Found a supplier of genuine replacements for around £12

Thanks again.
 