Any way to pump a PRV?

Discussion in 'Plumbing and Central Heating' started by DanRochester, 11 Apr 2012.

  1. DanRochester

    Joined:
    6 Mar 2012
    Messages:
    4
    Thanks Received:
    1
    Location:
    Kent
    Country:
    United Kingdom
    I have a customer who wants to have a new combi fitted in their basement.

    Have worked out a way to route the flue and can use a saniflo pump for the condensate.

    Am just wondering if there's any way to get around the PRV having to have a continuous fall?

    I would have asked this in the combustion chamber, but am waiting for my approval for the site to be granted. Am Gas Safe registered, before anyone posts a reply saying "get a registered guy in to do it".

    Many thanks,

    Dan
     
  2. mysteryman

    Joined:
    5 Jun 2010
    Messages:
    1,664
    Thanks Received:
    233
    Location:
    Shropshire
    Country:
    United Kingdom
    Drop it into the condensate pump. Check with Saniflo that it is OK with their pump; use another make if not.
     
  3. peekay53

    Joined:
    22 May 2011
    Messages:
    668
    Thanks Received:
    95
    Location:
    Merseyside
    Country:
    United Kingdom
    valiant do an extension to prv to get abovr ground level also worcester
     
  4. mickyg

    Joined:
    24 Aug 2005
    Messages:
    15,990
    Thanks Received:
    3,316
    Location:
    Hertfordshire
    Country:
    United Kingdom
  5. hansthebear

    Joined:
    24 Mar 2011
    Messages:
    603
    Thanks Received:
    69
    Location:
    Edinburgh
    Country:
    United Kingdom
    remote prv kit for potterton and baxi combis
     
  6. DanRochester

    Joined:
    6 Mar 2012
    Messages:
    4
    Thanks Received:
    1
    Location:
    Kent
    Country:
    United Kingdom
    Thanks guys,

    Have opted for a Baxi & their combined PRV & condensate pump.
    Pricey piece of kit but only one I found that specifically said that it's designed to do both.
     
  7. holty

    Joined:
    14 Jan 2006
    Messages:
    5,630
    Thanks Received:
    968
    Location:
    Cornwall
    Country:
    United Kingdom
    hate to say this, but even ideal logic do a remote prv kit

    p.s mysteryman. how do you think viessmann will best this solution where a condense pump is needed on the soon to be wb1c. for there combined condense and prv outlet?
     
  8. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,385
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    MM might have a problem answering that unless the MI have now been written!

    Perhaps it could be passed through a fanmy trap and then pipes in 32 mm plastic to the pump?
     
  9. holty

    Joined:
    14 Jan 2006
    Messages:
    5,630
    Thanks Received:
    968
    Location:
    Cornwall
    Country:
    United Kingdom
    they have. i mentioned this in the cc. think dan put a copy up i sent him.
     
  10. plumbswe

    Joined:
    28 Jan 2012
    Messages:
    256
    Thanks Received:
    20
    Location:
    Merseyside
    Country:
    United Kingdom
    3 bar prv on boiler plumbed into the return pipe. 22mm pipe teed off the return rising vertically until height of the flue then an external prv at 2.5 bar attached to this 22mm pipe then 15mm discharge ran off as normal. Baxi approved this solution and sold me the 2.5 bar prv. Check with your boiler manufacturer to ask if you could do the same.
     