Baxi 105e Boiler central heating not working, hot water fine

Discussion in 'Plumbing and Central Heating' started by DrGonzo98, 2 Sep 2009.

  1. DrGonzo98

    Joined:
    2 Sep 2009
    Messages:
    4
    Thanks Received:
    0
    Location:
    West Midlands
    Country:
    United Kingdom
    I'm new to this forum so please bear with me.

    I've moved to a new property that has an existing Baxi Combi Instant 105e Boiler. The hot water works fine but when I've tried to fire up the central heating it doesn't work.

    When I switch on the CH after 10 second the 'hot water tap symbol' flashes green, the ignition flashes yellow then goes solid. After about 12 seconds the 'hot water tap symbol' goes off and then about 30 seconds later the boiler stops. The radiators at no stage heat up.

    I've looked in the fault finding manual and the according to this the 'radiator symbol' should come on green to begin with instead of the tap symbol.

    Any suggestions of what the fault might be or anything I can try make it work / diagnose it further?
     
  2. EliteHeat

    Joined:
    28 Jan 2006
    Messages:
    1,094
    Thanks Received:
    2
    Location:
    London
    Country:
    United Kingdom
    How are you trying to start the heating?
     
  3. Rob

    Rob

    Joined:
    14 Aug 2006
    Messages:
    4,481
    Thanks Received:
    415
    Location:
    London
    Country:
    United Kingdom
    The flashing HW symbol is probably pre-heat. Meaning your probably not turning the heating on properly.

    Is the timeswitch in the on position? Is the room stat turned up?
     
  4. davebgas

    Joined:
    9 Feb 2009
    Messages:
    2,043
    Thanks Received:
    254
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Flashing HW light is boiler in pre-heat.
     
  5. gaspro1981

    Joined:
    7 Dec 2008
    Messages:
    1,594
    Thanks Received:
    257
    Location:
    Devon
    Country:
    United Kingdom
    so its a 105e instant :?:
     
  6. davebgas

    Joined:
    9 Feb 2009
    Messages:
    2,043
    Thanks Received:
    254
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Think the OP says it is in opening post mate
     
    • Thanks Thanks x 1
  7. gas4you

    Joined:
    23 Feb 2007
    Messages:
    17,962
    Thanks Received:
    864
    Location:
    Norfolk
    Country:
    United Kingdom
    Check all external heating controls are on. Check for 240VAC at the switched live terminal on the boiler.

    Also check the hw/ch knob has not broken, so will not turn on to ch.
     
  8. gaspro1981

    Joined:
    7 Dec 2008
    Messages:
    1,594
    Thanks Received:
    257
    Location:
    Devon
    Country:
    United Kingdom
    feck me spot on :oops:
     
  9. davebgas

    Joined:
    9 Feb 2009
    Messages:
    2,043
    Thanks Received:
    254
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Fault finding starts here...... does the CH demand light come on?
     
  10. baxpoti

    Joined:
    15 Dec 2006
    Messages:
    4,488
    Thanks Received:
    555
    Country:
    United Kingdom
    On the boiler incoming terminal block, locate terminals 1 and 2. Isolate , label and disconnect any wiring on here and link the terminals 1 and 2.

    Heating now works?
     
  11. davebgas

    Joined:
    9 Feb 2009
    Messages:
    2,043
    Thanks Received:
    254
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Baxpoti, you're probably the man to ask about a 105e if its ok to PM you?
     
  12. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,815
    Thanks Received:
    3,682
    Location:
    London
    Country:
    United Kingdom
    If Baxpoti has anything useful to say then he should say it here or in the CC !
     
  13. DrGonzo98

    Joined:
    2 Sep 2009
    Messages:
    4
    Thanks Received:
    0
    Location:
    West Midlands
    Country:
    United Kingdom
    Elite Heat / Rob 884

    I'm starting the heating by moving the switch on the the timer to the 'on continuous position as opposed to timer or off (if that makes any sense).

    There is an external control a thermostat on the landing. Some (not all) of the rads also have thermostat valves on them too
     