Baxi Duo-Tec E119 error code

Joined
30 Sep 2008
Messages
558
Reaction score
15
Location
Cleveland
Country
United Kingdom
Got an E119 code on my boiler.

Overnight the seal on my magnaclean appears to have sprung a leak and the pressure has dropped.

I've isolated the magnaclean, cleaned/refitted/refilled/bled, repressurised the system to 1.5Bar but the boiler will not fire up.

Have tried resetting with no luck. Any ideas before I call the guy that installed it back. Would rather have hot water now as opposed to later.
 
Sponsored Links
have u reopened the flow and return valves ? try taking pressure a bit higher sometimes these pressures switches are a bit sensitive.or failing that drain boiler check for debri in the pressure switch then fill boiler again.if u are sure pressure is right short 2 connections at pressure switch and see if boiler fires if so replace pressure switch
 