boiler runs for 30 seconds then cuts out

Discussion in 'Plumbing and Central Heating' started by peely, 20 May 2007.

  1. peely

    Joined:
    25 Apr 2006
    Messages:
    20
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    Hi
    I have recently fitted isolation valves in the feed and return to my Optia ff50 boiler, I also replaced the pump at the same time. The boiler now runs for a short time (30 seconds) before cutting out, it then sounds like water is trickling into the boiler, after about 5 minutes the boiler fires up for another 30 seconds then shuts down again.

    All rads/system have been bled and refilled.

    I am thinking that the bore of the isolation valves could be the problem?

    Any thoughts

    Peel :rolleyes:
     
  2. sooey

    Joined:
    10 May 2006
    Messages:
    10,244
    Thanks Received:
    652
    Location:
    Merseyside
    Country:
    United Kingdom
    Have you put the new pump on the right way around.
     
  3. peely

    Joined:
    25 Apr 2006
    Messages:
    20
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    wow
    thanks for the fast reply
    just had a double check and the big arrow on the side points the same way
    peel
     
  4. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,549
    Thanks Received:
    3,655
    Location:
    London
    Country:
    United Kingdom
    Same way as what?

    If you hear a trickling sound then that implies there is air inside and its not full of water! Bleed points???

    Tony
     
  5. peely

    Joined:
    25 Apr 2006
    Messages:
    20
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    I have bled everything "bleedable", several times,

    I have just double checked the the manual bleed on the "rad side" and just cracked the auto bleed on the hot water side, both full of water.
    Both are higher than the boiler, do you think I may need a bleed point closer to the boiler ?
    Pump is wired up the correct way as well.
    thanks for the help
    Peel
     
  6. gas4you

    Joined:
    23 Feb 2007
    Messages:
    17,911
    Thanks Received:
    850
    Location:
    Norfolk
    Country:
    United Kingdom
    Do you get air/water out of upstairs rads? Is f&e tank full?

    If so turn h/w on at timer, turn boiler off at stat, turn pump speed up to max and try to push air lock out to vent. Then try this with jusy ch on and only 1 rad left on, then do each rad in turn and see if this helps ;)
     
  7. peely

    Joined:
    25 Apr 2006
    Messages:
    20
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    getting water out of the rads, bit I'll give it a go

    seems that I am looking at an airlock rather than a valve problem?

    I might fit a bleed valve just above the boiler if I still get probs?
    what do ya think?

    Cheers
    Peel
     
  8. joineryisahobbynotatrade

    Joined:
    18 May 2007
    Messages:
    9
    Thanks Received:
    0
    Location:
    Glasgow
    Country:
    United Kingdom
    The trickling sound does sound like air.Bleed the pump and stick a screwdriver in to make sure it does not stuck CRUNCH CRUNCH
     