Can I use any make MCB B40 on my Crabtree C/U ?

Discussion in 'Electrics UK' started by zappastix, 15 May 2010.

  1. zappastix

    Joined:
    2 Oct 2007
    Messages:
    211
    Thanks Received:
    2
    Location:
    Sussex
    Country:
    United Kingdom
    :confused: Hi

    I need to change my MCB B32 to MCB B40 for a new shower.

    The C/U is around 12 years old.

    Will any make of MCB fit my Crabtree Star Breaker C/U ?

    For instance the BusBar?

    Many thanks.

    Stephen
     
  2. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    1. What size cable is it?

    2. Do you know what its current carrying capacity is given how it is installed?

    3. How will you verify that its R1+R2 is OK for a breaker of increased rating?

    4. Is the circuit RCD protected?

    5. http://www.diynot.com/wiki/electrics:part-p

    No. Ones other than the originals might fit, but it is absolutely not the case that any and all will fit.
     
  3. zappastix

    Joined:
    2 Oct 2007
    Messages:
    211
    Thanks Received:
    2
    Location:
    Sussex
    Country:
    United Kingdom
    Thanks ban-all-sheds.

    I just wanted to know if there are any physical differences between MCB's (B rated).

    This is because I have a long journey to screwfix/B & Q and don't want to find out there are differences and a different brand would not fit.
    I wanted to get he job done this weekend. If I have to order online then I'll do that.

    In answer to your concerns;

    I've spent hours looking into this.

    The cable is 6mm.

    6mm twin and earth cable is rated at 47 Amps at best. At 240V (real, not nominal).

    The old shower was 8.5kW.

    The MCB for the old shower is B32.

    We have lived here for 7 years and the shower has never tripped.

    90% of the cable is in an airy/large loft.

    Showers up to 8.5kw may carry a 6mm cable as long as the shower unit is within 18 meters of the fuseboard. Fuses and switches should be rated at 40 amps.

    It is because it seems the person who fitted the MCB for the shower didn't seems to fit the correct rating MCB, is why I want to change this for B40.
    In saying this - maybe Regs years ago were different.

    My electric oven is on a MCB B32 running on 6mm cable - no problem there.

    Thanks.
     
  4. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    There are.


    And 23.5A at worst.


    The other 10%?
     
  5. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,743
    Thanks Received:
    1,228
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes, but the oven won't be pulling 32amps and if it did then not for too long as it has thermostats and stuff.

    Electric showers are wham 37amp all the time until you turn them off devices so overloads and tripping of mcbs are likely unless the circuit is designed properly.

    What is the R1+R2 for the 6mm circuit?
     
  6. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    423
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    TTC genuine interest and wanting to learn and understand. If i have understood your last response correctly why does knowing what the R1+R2 is, which i understand is a continuity check between phase and earth, impact/effect/influence the choice of MCB.
     
  7. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    • Thanks Thanks x 1
  8. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    423
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    Thanks BAS, I need to read that link in detail to get my head around the inter relationships of the Zs , Ze etc but with this topic example it will make more sense.
     
  9. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    Zs = Ze + (R1+R2).

    Or Ze + (r1+r2) for a ring final.
     
  10. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    Zs = Ze + (r1+r2)/4 for a ring final circut ;)
     
    • Thanks Thanks x 1
  11. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    Got them the wrong way round.... :evil: :oops: :cry:
     
    • Thanks Thanks x 1
  12. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    423
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    Thanks to both. A further question, if the calculated Zs result is different to the actual measured result, does it signify a problem or is it ok as long as the actual result is within the limits of the tables.
     
  13. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,743
    Thanks Received:
    1,228
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Measured and calculated are often slightly different. Its OK as long as within the EFLI limits. And don't forget the rule of thumb.
     