Work up this morning to zero pressure water in the boiler, I think i have a sticking relief valve.
are these easy to strip and clean and rebuild?
It looks almost accessiable, any thing to watch out for?
do they have easily available seals inside?
I`m at work so no boiler name and number.
thanks
Ray
 
Sponsored Links
Sponsored Links
I do have water dripping from the relief valve, this morning i went around the underfloor area and checked all the joints for leaks, then i repressurised the system to 1 bar on the dial and switched the heating on, after 10mins i had 3 bar and the valve had been releasing water.
i reduced the cold pressiure to about 0.8 bar and when hot the pressuire
was around 2.5 bar.
what i am thinking is that the valve has been opening fairly often and has something stuck in it or a seal has failed.
Also the plumber who fitted the boiler said run it at 1.5-2bar cold, it appears this is too high when hot, maybe the problem.
am i barking up the wrong tree? looked at Faq`s and i will try that in the morning.
maybe a hamlet moment if i can fix it?

Ray
 
You are getting water from your pressure relief because your expansion vessel is fooked :)
 
Drain your system to 0bar pressure (when cold).

Press the pin on the schrader valve and see if water comes out, if it does your diaphram is split.

If a bit of air comes out, put a pike pump with a pressure gauge on and see if the pressure is to the correct level (it should say on the expansion vessel the correct bar)
 
Drain your system to 0bar pressure (when cold).

Press the pin on the schrader valve and see if water comes out, if it does your diaphram is split.

If a bit of air comes out, put a pike pump with a pressure gauge on and see if the pressure is to the correct level (it should say on the expansion vessel the correct bar)

a pike ,will he tarmac my drive afterwards?

we could do this all day :D
 
Assuming the expansion vessel is knackered, is there such a thing as a universal expansion vessel that could be fitted, possibly externally.

The replacment is between £120 and £200, and would a non standard one be cheaper?
The spec is 8ltr and 1 bar.
Cheers

Ray
 