    Hello,

    Would be grateful for people opinions on this situation I am in....

    The Client has requested a 17th edition consumer unit upgrade due to a child receiving an electric In the house. I visited the house to get an idea of what's going on etc.. the gas and water main have a 6mm earth tagged onto them. However, the client has limited funds and can only afford a fuseboard change including testing. Will take an extra day to upgrade the bonding to 10mm as laminate flooring/concrete floors are everywhere! With the supply characteristics that's present, would I be able to leave it at 6mm. Tncs system, main fuse 60a 1361. Or could I put it as a limitation on the certificate? Upgrade of equipotential bonding to water main and gas main in 10mm could not be carried out at present???

    Carl
     
  2. holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  3. Carloss

    Joined:
    31 Mar 2004
    Messages:
    168
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks, sorry for sloppy posting, using my phone to write this!

    Would it be acceptable if I carried out a continuity check on the bonding if I get readings below 0.05ohms would be acceptable? taking into consideration the type of earthing system and fuse size?

    Thanks,
    Carl
     
  4. holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  5. matt1e

    Joined:
    13 Dec 2008
    Messages:
    2,227
    Thanks Received:
    231
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    They may be ok if the system is TT
     
  6. londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    The installation is TNCS.

    I beleive you can verify 6mm by using adabatic equation.
     
  7. holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  8. matt1e

    Joined:
    13 Dec 2008
    Messages:
    2,227
    Thanks Received:
    231
    Location:
    Tyne and Wear
    Country:
    United Kingdom
    :oops:

    allright I'll go and clean me specs :LOL:
     
  9. holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  10. ebee

    Joined:
    14 Aug 2005
    Messages:
    1,702
    Thanks Received:
    29
    Location:
    Lancashire
    Country:
    United Kingdom
    TNC-S (PME) requires 10mm min (even then your supplier might require more)
     