    when wiring up a new electric oven which is on its own MCB (which was isolated), i found that when i cut into the cable at the length i wanted, it tripped out the RCD. when continuity tested with test meter, i found continuity between earth and neutral. Is this what you would expect to find and can anybody explain why i am getting continuity between earth and neutral?

    Thanks
     
  2. flameport

    Joined:
    10 Mar 2007
    Messages:
    4,622
    Thanks Received:
    744
    Location:
    Bournemouth
    Country:
    United Kingdom
    Even with the MCB off, earth and neutral are still connected. Your RCD is designed to operate when there is a N-E fault within your installation, such as you cutting through a cable.

    In most installations, E & N are connected together in one or more places - the supplier cutout, in the road outside, or at the substation supplying your property.
     
    • Thanks Thanks x 1
  3. Guitarguy

    Joined:
    26 Mar 2009
    Messages:
    185
    Thanks Received:
    8
    Location:
    Wiltshire
    Country:
    United Kingdom
    if the house is on a PME supply, the neutral and earth is one conductor in the supply cable and both the neutral and earth tails go into the neutral side of the electricity companies cutout. That would explain continuity
     
    • Thanks Thanks x 1
  4. cantab

    Joined:
    11 Sep 2009
    Messages:
    38
    Thanks Received:
    1
    Country:
    United Kingdom
    EDIT: What I wrote in this post is WRONG, so ignore it. Others have explained why.

    If the RCD tripped when you cut the cable then I reckon that cable was LIVE, and you're lucky to be (a)live yourself.

    I'm no spark, but I think RCDs trip if there's a current imbalance between live and neutral. A dead circuit should have zero current in both.
     
  5. londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    If it was live he woulda known about it!! N to E caused fault.
     
  6. cantab

    Joined:
    11 Sep 2009
    Messages:
    38
    Thanks Received:
    1
    Country:
    United Kingdom
    Can you explain? Sorry, I'm a bit confused here. Am I wrong in how an RCD works?

    If a circuit's dead, there should be no current flowing in either live or neutral, right. Thus, shorting neutral to earth, still no current. Am I missing something?

    (EDIT: You're right that if one cuts through a live cable that should be very obvious. I'm just trying to see how cutting a dead cable would cause anything to trip.)
     
  7. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    [​IMG]


    [​IMG]

    [​IMG]
     
    • Thanks Thanks x 1
  8. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    Yes - the fact that all the neutrals (on the RCD side) are connected together at the CU, so shorting one of them to earth shorts all of them....
     
    • Thanks Thanks x 2
  9. BS3036

    Joined:
    24 Sep 2007
    Messages:
    666
    Thanks Received:
    19
    Country:
    United Kingdom
    As flameport mentioned, the MCB doen't switch off the neutral. The neutral will have a small voltage on it caused by current flowing through the (small) resistance of some part of the neutral cable. So if you join neutral to earth through a very small resistance it is easy for between 15 and 30 mA or more to flow from neutral (and not in the live), ie enough to trip the RCD.

    Oh well. :)
     
    • Thanks Thanks x 2
  10. cantab

    Joined:
    11 Sep 2009
    Messages:
    38
    Thanks Received:
    1
    Country:
    United Kingdom
    Ah, I see. Thanks.
     
  11. Johnmelad502

    Joined:
    23 Aug 2008
    Messages:
    2,923
    Thanks Received:
    50
    Location:
    Cumbria
    Country:
    United Kingdom
    Wow, that was sooooooooo helpful. :mad:
     
  12. davelx

    Joined:
    26 Sep 2006
    Messages:
    1,223
    Thanks Received:
    73
    Location:
    London
    Country:
    United Kingdom
    What BAS is saying is that unless you KNOW what you are talking about then better to keep quiet and learn from those who do.
     
  13. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    Not necessarily - sometimes doing or saying something that makes you look a right plonker can be a spur to learning things so as not to look a plonker again..
     
  14. cantab

    Joined:
    11 Sep 2009
    Messages:
    38
    Thanks Received:
    1
    Country:
    United Kingdom
    Indeed :oops:
     
  15. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    51,596
    Thanks Received:
    2,018
    Location:
    London
    Country:
    United Kingdom
    My words were a bit ill-chosen - I didn't think that your mistaken post made you look a "right plonker" - that's definitely too excessive - sorry about that....
     