works fine on ch but on dhw boiler fires and flow pipe gets hot not dhw. motor on valve works fine(pin moving) and valve has been refurbished with black nut and pin kit. p2p is full of crap but would this result in hot water going to rads??
 
Sponsored Links
if its almost totally blocked then the excess pressure on the diverter valv e will cause the valve to leak into the heating circuit.

Obviously it needs cleaning or replacing.

Tony
 