On this TT supply I have a measured Zdb (all parallel paths in place) of 154? and yet the measured Zs on the ring (using RCD setting on my Metrel) is consistently below 1?. Can anyone explain how that can be?[/wiki]
Something seems amiss there, probably the meter.
What's the R1+R2 value for the circuit? This added to your Zdb should be similar to the Zs figure you get when measuring at the furthest point.
I'd say you still have an appliance on the ring still connected when you do the Zs and it is providing a parallel path eg boiler (earth of boiler connected to water pipes, maybe main water pipe is metallic in ground so providing a path)
Daft as it sounds, you have made sure the CPCs of the ring are in the CPC rail of the CU? I'm thinking you may get low readings like this if they have accidentally been connected to the neutral rail.