Honeywell 3 position diverter valve clicking (V4073A1039)

Discussion in 'Plumbing and Central Heating' started by MarkyMark76, 4 Jan 2008.

  1. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Howdy again,

    Seems it's all falling apart at once in my plumbing system!

    When the boiler is running the 3 position diverter valve has started "clicking". The clicking noise is the microswitch being hit then the valve moving off it and then moving back and making contact with the switch again. A sort of rocking motion that means the microswitch is being hit every second or so.

    It happens when only the hot water is on and when the hot water and central heating is on. When only the central heating is on there is no problem.

    Any ideas?!
    Thanks.
     
  2. ChrisR

    Joined:
    24 Jul 2003
    Messages:
    23,600
    Thanks Received:
    1,142
    Location:
    London
    Country:
    United Kingdom
    They do this clicking when in the mid position, if there's something wrong with the bits on the pcb in there. The motor's supposed to "stall".

    But on HW only , it shouldn't be in the mid position, it should be fully returned.

    SO forst check your wiring - there must be a conection from the "hw off" terminal of the programmer as well as the cylinder stat, to the grey wire.

    If the woring's ok, change the head of the valve. If you leave them doing the rocking/ticking thing, they wear the shaft which leaks then you have to change the whole valve.
     
  3. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Thanks for the tips. Will take a look over the weekend hopefully!

    Any idea what sort of money is involved in the spare parts or the whole valve?
     
  4. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Checked the connections and some voltages today and found the following -

    Only in the "down" position for CH only -
    [​IMG]

    ~230V going to grey wire at this point. Then turn the thermostat on the HW and the valve moves to the mid point where it stalls and starts clicking. At this point the voltage jumps between 230V and 0V (at least i think it goes to 0V, my DVM is a bit slow to respond...)
    [​IMG]

    Doesn't matter if its HW only or HW and CH this is the position is sits untill the boiler switches off. Now and only now does the valve go all the way to the "up" position. If the HW switches off and the CH is still running then the valve returns to the bottom position. As soon as the HW engages, regardless of CH setting, then it goes to mid position and gets clicking!

    Does this sound like something in the electronics on the valve is bust? Thanks again for assistance!
     
  5. doitall

    Joined:
    8 Jan 2005
    Messages:
    19,007
    Thanks Received:
    1,536
    Location:
    Bath
    Country:
    United Kingdom
    AS Chris said probably a wiring problem, which should be tested as follows.

    No power on valve HW only port B open.

    240V on white wire HW + CH mid position.

    240V on white and grey CH only poart A open 240V on orange.

    240 on grey wire is valve held in last position, but if last position was CH approx 100V on orange wire
     
  6. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Thanks for that info.

    Problem is it never gets to a static mid position. Whenever it goes to the mid point the clickings starts. Will check the voltages as you suggest later.
     
  7. doitall

    Joined:
    8 Jan 2005
    Messages:
    19,007
    Thanks Received:
    1,536
    Location:
    Bath
    Country:
    United Kingdom
    Thats why you should check for power on the other wires, in the mid position only the white should have 240V
     
  8. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Not convinced my voltage measuring techniques are quite according to the text books so time to get in a proffesional.

    As far as i can tell from the diagram and the assortment of wires in the control box they all match up correctly. Coupled with the fault only starting late last year and we've lived here for 4yrs now makes me wonder about the wiring being the route cause but what the heck do i know! :(

    Thanks to all who have submitted advice and suggestions. This site is pretty awesome. Sadly i am let down my own lack of any useful practical skills!! :LOL:
     
  9. doitall

    Joined:
    8 Jan 2005
    Messages:
    19,007
    Thanks Received:
    1,536
    Location:
    Bath
    Country:
    United Kingdom
    Just buy a new head and stick it on, for around 12 quid could save you a lot a hassle
     
  10. chad5k1

    Joined:
    6 Jan 2008
    Messages:
    31
    Thanks Received:
    0
    Country:
    United Kingdom
    Where do you find a head for £12?

    The cheapest I've seen one is about £50 trade price, but maybe I'm looking in the wrong places.

    Thanks very much in advance.
     
  11. doitall

    Joined:
    8 Jan 2005
    Messages:
    19,007
    Thanks Received:
    1,536
    Location:
    Bath
    Country:
    United Kingdom
    Bit more than that :eek: the 6 wire actuator is 40.52 at BSS.
    3 wire 56.48 & 5 wire 64.38.
     
  12. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Got one for 58GBP delivered so will wait and see if this fixes it.

    Thanks again!
     
  13. chad5k1

    Joined:
    6 Jan 2008
    Messages:
    31
    Thanks Received:
    0
    Country:
    United Kingdom
    let us know MarkyMark76, as I have the same issue :)
     
  14. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    No problem, should be here today or tomorrow.
     
  15. MarkyMark76

    Joined:
    3 Jan 2008
    Messages:
    14
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    Hurrah!! We are now fully operational "clicking" free!! :D

    Although the cnut that put the valve where it is will get a reet hard slap if i ever meet him!! :LOL:

    This evening i also learnt that 240V will give you a right good 'tickle' if your not paying attention... :oops:
     