    Hi,

    Another dreaded Isar HE 35 from what I've read on forums. It's just over 3 years old, using an original black PCB. Already had a replacement expansion vessel under warranty.

    Currently DHW is working fine but CH isn't.

    As it's now getting chilly in the evenings, I thought i'd fire up the boiler for CH. Turned the timer on, waited 10 mins and checked all rads. no joy.
    I thought it was a stuck TRV like last year but i think it's ok - Removed TRV head, pin doesn't look stuck and tapped the valve body a few times with a pin hammer.

    Turning the boiler on (or switching from DHW to CH), I can hear a clicking/ticking sound which makes me believe it's the diverter valve/actuator at fault. The burner does fire up though for CH for about a minute or so until it goes off. I assume overheat protection?

    Switching from CH to DHW, same ticking noise and the burner doesn't fire until the ticking has stopped.

    So, anything else I can rule out before getting a parts/engineer to fix?

    On another subject, if I got the Ideal fixed price engineer to come and fix, would they also replace the PCB to the new orange ones when my current one isn't faulty?

    Cheers all.

    Ray
     
  2. ChrisR

    Joined:
    24 Jul 2003
    Messages:
    23,582
    Thanks Received:
    1,142
    Location:
    London
    Country:
    United Kingdom
    Very likely. Not too hard to change .

    Re the pbc, it would depend whether it had had an "accident" or not. ;)
     
  3. corgikiller666

    Joined:
    21 Sep 2009
    Messages:
    49
    Thanks Received:
    17
    Country:
    United Kingdom
    before anything else are you sure you have no dripping hot taps or leaking hw pipes?
     
  4. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,402
    Thanks Received:
    3,639
    Location:
    London
    Country:
    United Kingdom
    You can easily prove the latter by turning off the cold feed into the boiler.

    If that does not solve the problem then it does sound like a jammed/failed diverter valve.

    Tony
     
  5. RayLee

    Joined:
    26 Sep 2009
    Messages:
    2
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    no leaking/dripping taps. always displays 0 unless i'm using the HW (d) or CH (c)
     
  6. swiftyboy

    Joined:
    4 Mar 2010
    Messages:
    1
    Thanks Received:
    0
    Location:
    Glasgow
    Country:
    United Kingdom
    I too have the same problem, I have DHW no CH with the control displaying 0, I have just replaced the PCB to the newer orange on and fitted the pins in the correct order ( confirmed when switching on I get a 4 displayed for 1-2 seconds )

    I dont seem to have any leaks anywhere and all the radiators have been bled, how can I checked the divertor valve to see if it has stuck or jammed

    getting very cold up here now any help would be very much appreciated.

    cheers
     
  7. onlyfitidealboilers

    Joined:
    11 Jan 2010
    Messages:
    2,022
    Thanks Received:
    151
    Location:
    Aberdeen
    Country:
    United Kingdom
    just ring your local RGI mate he will sort it. :D
     
  8. Temprise

    Joined:
    19 Nov 2009
    Messages:
    228
    Thanks Received:
    58
    Location:
    Berkshire
    Country:
    United Kingdom
    Does the boiler always show 0 in the display, even when your external timers and room stat are on and calling for heat?

    If this is the case then you will have a problem with your external controls (faulty timer, room stat or wiring problem).

    Regards.
     
    • Thanks Thanks x 1
  9. nogoodatfaultfinding

    Joined:
    10 Dec 2008
    Messages:
    857
    Thanks Received:
    72
    Location:
    Yorkshire
    Country:
    United Kingdom
    First thing i would check as well in this situation
     
  10. Garfeild

    Joined:
    19 Jan 2007
    Messages:
    1,128
    Thanks Received:
    130
    Location:
    Kent
    Country:
    United Kingdom
    6 month old thread
     