Installing a new 32a circuit for cooker

Discussion in 'Electrics UK' started by rizla01, 20 Mar 2013.

  1. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Hi,

    Can someone tell me if a leccy is meant to test a 6mm 30a circuit before connecting and if so what tests should have been carried out?

    Installation was a 32a RCD, 6mm run of cable (4Mtrs) to isolater switch, then connection to outlet and then to cooker.
     
  2. ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,347
    Thanks Received:
    383
    Location:
    Gloucestershire
    Country:
    United Kingdom
    If it was a new circuit then you should have received an EIC which will include test results as well as a schedule of inspection. Also signature responsibility for design and construction
     
    • Thanks Thanks x 1
  3. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Leccy has't finished the job yet as he has a mains circuit to extend for the kitchen.

    Just that I watched the whole install of the 30a circuit right through to connecting the cooker which was then switched on. That was that.

    Perhaps he has done so many and as it was all new wiring, he didn't feel the need to test anything.

    Can you tell me (So that I sound like I know what I am talking about) just what tests should be done on the extended ring main?

    I realise that I will get a certificate but I would like to know and it doesn't feel right asking him.
     
  4. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,807
    Thanks Received:
    1,237
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Table 8.5 - Correct sequence for safe testing
    BEFORE CONNECTION OF THE SUPPLY
    1 Continuity of protective conductors
    2 Main and supplementary bonding continuity
    3 Continuity of ring final circuit conductors
    4 Insulation resistance
    5 Connect ring in 'figure of 8' configuration and carry out R1+R2 measurements at CU and at every socket outlet
    6 Polarity

    WITH THE SUPPLY CONNECTED
    7 Confirm correct polarity
    8 Earth-fault loop impedance
    9 Correct operation of residual current devices
    10 Correct operation of switches and isolators / functional testing

    There may be other tests needed, depending on the supply type.
    The results of the above tests will be recorded on the Installation Certificate
     
    • Thanks Thanks x 1
  5. ericmark

    Joined:
    27 Jan 2008
    Messages:
    8,957
    Thanks Received:
    768
    Location:
    Flintshire
    Country:
    United Kingdom
    What Taylortwocities says is correct but it is quite common to miss some tests out however to be able to fill in the paperwork he will need to use a loop impedance meter.

    Some firms don't provide all their electricians with the test gear and have an electrician who calls in at each site and does inspection and testing.

    Fudging up results for the paperwork can really cause problems latter on. What we should do is before testing look at previous test results and then compare with new results to see if the circuit is degrading.

    The RCD should also be tested with a special meter which not only tests that it works but measures the time it takes to work which should in most cases be under 40ms.

    Maybe you should ask him if he can show you what a loop impedance tester looks like as you have heard about them but never seen one. Then see what he says?
     
    • Thanks Thanks x 1
  6. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Thanks all, for the advice and info. Good to know what I am paying for and to know what to look out for.
     
  7. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom


    Just as an aside, do many installations actually fail? (Poor cable, insulation, Sockets, Etc) on a new install?

    Al that testing seems to be overkill when compared to days of yore when it wasn't done.

    I agree entirely with the correct routing of cables, earthing Etc etc but how necessary is all the rest, in true reality?

    NOT asking for a lecture here, just inquisitive. :)


    Anyone?
     
  8. EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    11,901
    Thanks Received:
    1,347
    Location:
    Dorset
    Country:
    United Kingdom
    They may not 'fail' but it shows up mistakes or that none has been made.
    Perhaps it is for one cable.
    So which test(s) would you omit?

    If testing is not done, you wouldn't know it didn't really need doing, would you?
     
  9. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    So would you say that the majority of these tests are checking human error more than product failure?
     
  10. EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    11,901
    Thanks Received:
    1,347
    Location:
    Dorset
    Country:
    United Kingdom
    Not the majority - no. Some are both.

    The list may look daunting (I don't know your experience) but they don't take long to do.
    It's good to know that all is well and you haven't made a mistake.

    I ask again, which would you omit?
     
  11. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Well, I would have thought a lot of the faults tested for would show themselves up pretty quick (Blue flash, Smoke, CU tripping) but I am sure that a few could show up only under certain , fairly unlikely, conditions, but that they have to be tested for regardless

    Not being a Leccy I wouldn't know quite which ones.
     
  12. EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    11,901
    Thanks Received:
    1,347
    Location:
    Dorset
    Country:
    United Kingdom
    Ah, but that's the point.

    Blue smoke, flashing and cu tripping are not a good way to test and are to be avoided.

    By testing with a meter before energising these events can be predicted and prevented.

    Wires melting and the need to redo the circuit are not desirable so a quick test will show that it won't happen.
     
  13. rizla01

    Joined:
    13 Jul 2007
    Messages:
    38
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    But my point is that once connected and switched on. assuming there are no obvious faults showing within 2 mins, the likelyhood of any faults are extremely thin, surely.

    The only checks that are likely to be needed in most cases are earth faults and rev polarity checks Etc - both of which may not show immediately but that a basic test rig (Mains socket tester) would show up.

    Other than these easily noticeable faults, other failings would surely be almost unheard of.
     
  14. EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    11,901
    Thanks Received:
    1,347
    Location:
    Dorset
    Country:
    United Kingdom
    But my point is that switching on and waiting two minutes to see if anything goes BANG or melts is not a good way to verify the safety of electrical circuits.

    But that is what should be done.
    How many other of the tests do you include in 'etc.'.

    Socket testers are used when the circuit is energised so it may be too late and they cannot distinguish between Neutral and Earth so earth faults and reversed N and E would not be noticed.
    That is why tests are done prior to energising with something that can?
    Nor can socket testers be used at a cooker connection point.

    Also, your original post seemed to be complaining that the electrician had not carried out any tests which he should have done.
    Perhaps he 'just knew' everything was alright.

    But they are not easily noticeable and would not affect the operation of an appliance.
    Yet when something goes wrong they would be dangerous.
     
    • Thanks Thanks x 1