To be fair though, if i had this tar problem and some went on my nice new carpet/wood floor I'd not be very impressed and the DNO surely would have a case to answer and a cleaning/replacement fee to pay?
 
If it was sticky liquid tar, yes.

But I expect fully that this tar is rock hard and old.

Lets ask the OP to finger print test it.
 
It's as tacky as jelly sweets left out in the summer sun. :rolleyes:

You can press yer prints in.
 
Sponsored Links
Supply is TN-S, as stated.

Cable is hessian covered PILC, Paper Insulated Lead Covered.
- The paper is saturated in oil which does seep out, perfectly normal
- Hessian may be quite tarry to aid its insertion through your duct

Note PILC is not "armoured" in the conventional sense.
- Underground you will find the cable with bare lead exposed
- A spade will happily cut & short PN before your BS1361/BS88 fuse
- Assume PSSC outside london is 16,000A, inside london 24,000A

PILC requires care.
- Lead cubic crystalises over time making the cable fragile to splitting
- Never move a PILC supply cable, it is not your cable anyway

Weeping like that photographed is quite normal, indeed you are quite lucky the area is not sodden with oil/tar as many old properties. The only time a DNO is interested is a) if the cable or cutout are warm b) your cutout is metal (or metal & double fused) c) a large quantity of oil is found. Otherwise PILC is replaced a) when it goes bang or b) when you pay for it.

Generally PILC fails at the terminations, typically old pitch filled metal cutouts. Those should have long been replaced - if not then do contact the DNO. DNO will require MEB upgrading if they come out and do meter-change, supply cable change, incidentally. Typically 25mm tails & 10mm MEB (16mm if cable run outside re sized for mechanical protection and some even choose 25mm outside because it covers you if the insulation is damaged since 25mm can be non insulated re BS7671 compliance).

PILC will someday require a phased replacement, something DNOs tend not to think about because nationally it is much more costly than water/gas where a new pipe can be pushed through the old one. Many PILC have been in service 80yrs and are still fine, so I guess it will not be an issue before 2020-2040 for the earliest installed cables. Comes down to soil thermal conductivity, current loading & other mitigating factors. I expect loop-in supply (2 properties off 1 cable) may be the first to show failure, because of electric shower in each property & electric cooker.

With underground distribution faults (PD, Partial Discharge), they boost the current briefly (called thumping) to detect where to effect cable repairs (by standing over the area and it goes thump). Those PILC cables are monitoring whilst the cables are online and likewise come under the maintenance strategy. We have a lot of old infrastructure in the UK, the (super)grid is old, the generating plant is a bit lacking with oil prices likely to push people from oil-boilers to electric-boilers, and overall it was designed in the 1950s & u/g thro the 1970s.
 
Just to follow up on this tar issue:

We were due to go partying on Saturday night, first time since we moved in really, I could smell that pungent whiff. At the time my little lad was in the shower (8kw) and missus tarting herself up (hairdryer 1800w). There was an audible crackling at this cut-out and whisps of smoke.

Scot Pow called out... 30 minutes later two guys arrived... a further 30 minutes new cut-out fitted and all powered up again.

Loose connection on load side of cut-out fuse.


Regards
UF
 
Yes please, the sparkies need some more sparky porn :D
 
BUMP. BUMP. Ok... wait for it, wait for it... splurge your population paste over this one! :rolleyes:






jerkit5.gif








S8002983.jpg



Anyone spot a missing seal?

Regards