MAIN combi 24 HE

Joined
23 Dec 2010
Messages
3
Reaction score
0
Location
Manchester
Country
United Kingdom
condensation pipes had frozen this morning and backed up into the boiler trap, Ive successfully defrosted and drained all the water. The problem now is the FLAME failure light is permanently lit, no noise or anything happening :cry:
 
Sponsored Links
A contact at the top of the condensate pipe checks that the trap is not full.

Either yours still is or its just still wet on the surface.

Tony
 
ive fully drained the trap and now disconnected the 2 teminals, both dry but gonna leave them off for a bit to make sure. See how that goes
 