    I have a main medway automatic which supplies a shower through mixer taps. The hot water is ok through the normal taps but not through shower. Is the problem likely to be the diaphragm and if so is it easy to replace? Has anyone got MIs
     
  2. Paul Barker

    Joined:
    4 Aug 2005
    Messages:
    9,631
    Thanks Received:
    869
    Location:
    Yorkshire
    Country:
    United Kingdom
    MI's are available on the Baxi website Main belong Baxi. I know that because when I was trying to fix one and rang Baxi for service information the nice man said that they are definately on there but hard to find. I never did find them but they are there.

    Failing that ask them to send you a copy.

    Is it the diaphragm? Depends what flow rate from the other tap inspires it to light, then check with Baxi if that is correct, if not fit a diaphragm.

    I'd sooner have a Brittony II to change the diaphragm on.

    You'll probably knacker the two small copper pipes and will need a new seal which the pin slides through, and have to take the whole thing off and on a few times before you have it leak free again.

    GOOD LUCK, horrible machines.
     
  3. ChrisR

    Joined:
    24 Jul 2003
    Messages:
    23,582
    Thanks Received:
    1,142
    Location:
    London
    Country:
    United Kingdom
    Here http://www.partsarena.com/baxi/

    you will find all these:

    Basic (Later Production) (GC No. 5247625)
    Medway Super L (GC No. 5247641)
    R (Late Production) (GC No. 5247628)
    Super (GC No. 5247639)

    Is the "Automatic" a different one?
     
  4. ollski

    Joined:
    8 Oct 2003
    Messages:
    4,982
    Thanks Received:
    72
    Location:
    Birmingham
    Country:
    United Kingdom
    Always thought the medway automatic was only for lpg?
     
  5. ChrisR

    Joined:
    24 Jul 2003
    Messages:
    23,582
    Thanks Received:
    1,142
    Location:
    London
    Country:
    United Kingdom
    Went into Identiffier and it looks like you're right Oilski. Automatic only listed for LPG. Parts Numbers for diaphragm etc are not same as any of the others I looked at.
     
  6. superskanker

    Joined:
    11 Jul 2006
    Messages:
    49
    Thanks Received:
    0
    Location:
    Manchester
    Country:
    United Kingdom
    The hot water is ok through the normal taps but not through shower


    probably the shower thermostat then, assuming its a thermostatic shower
     
  7. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,402
    Thanks Received:
    3,639
    Location:
    London
    Country:
    United Kingdom
    Clearly ( to me ) the flow rate through the shower is not sufficient to turn the water heater on.

    Confirmation by measuring the flow rate through tap and then through shower.

    Solution to either clean the holes in the shower head or drill them out to increase the flow rate.

    Proper solution, measure flow rate and then change diaphragm if heater needs more than 2.5 li/min to turn on.

    Tony Glazier
     
  8. btic

    Joined:
    15 Aug 2006
    Messages:
    3
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    The shower works off a mixer tap regulated by a governor on the cold feed. The same problem occured 6 months ago and I replaced the shower mixer and head which worked. The governor has also been replaced in the last few years. Hence everything between shower head and water heater are relatively new which seems to point to diaphragm unless mixer/governor have gone faulty
     
  9. OllieN

    Joined:
    31 May 2006
    Messages:
    61
    Thanks Received:
    0
    Location:
    Bournemouth
    Country:
    United Kingdom
    Could it just be build up of limescale in the shower head restricting the flow (hence the new shower head fixed it 6 months ago)? Maybe just try descaling the head for a quick fix?

    Sorry Tony, just read your post and you've already suggested this.
     
  10. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,402
    Thanks Received:
    3,639
    Location:
    London
    Country:
    United Kingdom
    I think that the further information may be a significant clue!

    Can you adjust the outlet pressure on the regulator to significantly reduce it.

    Tell us what this does.

    We also need to know the water flow rate at which the heater turns on when just a hot tap is turned on.

    Tony

    PS Great minds think alike Ollie !
     
  11. btic

    Joined:
    15 Aug 2006
    Messages:
    3
    Thanks Received:
    0
    Location:
    Merseyside
    Country:
    United Kingdom
    As an eplilogue:- finally the shower got too cold so I replaced the diaphragm. It was easier to take the unit off the wall and turn upside down to remove 8 screws to bottom plate of water regulator Everything seems to work ok now. Thanks to any contributors.
     
  12. sasibhushanp

    Joined:
    3 Jan 2007
    Messages:
    1
    Thanks Received:
    0
    Location:
    Middlesex
    Country:
    United Kingdom
    Hi,
    I have the Medway Super GC No 5247639 Gas fired water heater. I have the problem as 'btic' mentioned. I am not getting HOT water in the Shower.

    Do you know any company who can do servicing this water heater in Middlesex Area? If so, please let me know their Website address as well as their contact telephone details.

    Rgds,
    Sasi
     