Mains cable/Alarm cable in same conduit
26 Jan 2014
Glasgow
Hi there. If I were to run 12-15 Mains T&E cables in the same conduit as approx 10 6 core alarm cables is there a chance of false alarms as a result of capacitive coupling?
If so are there any steps I can take to reduce the chances?
Regards
Is the alarm cable shielded or unshielded? Its always best to avoid long parallel runs, but I cant say I have ever had false alarms due to this (I have a few installations where this was unavoidable). Are you laying the mains cable or the alarm cable btw?
Thanks for reply
I've a 100m roll of unshielded. I'm relocating the alarm panel from skirting level at front door to cupboard under stairs. the longest parallel run would only be about 2 meters
Many thanks
ah ok, you made it sound like you was going to be running the mains cable :p So I was going to mention derating of the circuits etc... lol I cant imagine you would get much of an issue with interference. It might not be possible but can you place the panel on the other side of the cupboard and have its own trunking/conduit? That certainly would help any possible interference and/or disruption should there be any electrical work where the alarm cables might get damaged etc..
I can't answer categorically but I was taught never to do that, only to cross at 90 degrees, never had a problem
Mains cable should be ran separate to alarm cable otherwise you will get enduced ac voltage on your alarm cables which can cause false alarms when lights are turned on or central heating starts up etc ?
If you get at multimeter and set range to ac and put positive probe on 12v positive and the negative probe on earth.If you get a reading of more than 2 volts ac then that is bad news.
You can use a 1313 filter to reduce the ac induced voltage.
Also depends on control panel make.Some control panels are worst than other for main interence(gardtec 500,800 series,scantronic)