    does anyone know please if it is possible to test the value of the earth rod resistance Ra I believe using a 3 lead tester on an efli robin tester because the niceic book and other literature i have seen only shows a 2 lead tester on phase and earth rod ? any suggestions

    Thankyou :confused:
     
  2. sparkybird

    Joined:
    19 Jan 2005
    Messages:
    1,168
    Thanks Received:
    40
    Country:
    United Kingdom
    yes, IIRC look in Guidance Note 3 (testing and inspection) at method 2 for Ra testing.

    Someone has nicked my copy or else I'd tell you the page!

    SB
     
  3. TONY144

    Joined:
    16 Feb 2006
    Messages:
    44
    Thanks Received:
    0
    Location:
    Staffordshire
    Country:
    United Kingdom
    thanks will look

    cheers

    Tony
     
  4. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    Put the black test lead on Neutral ;)
     
  5. TONY144

    Joined:
    16 Feb 2006
    Messages:
    44
    Thanks Received:
    0
    Location:
    Staffordshire
    Country:
    United Kingdom
    That will give the ze reading i believe and not the resitance value of the earth electrode but correct me if i am wrong
     
  6. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    What is the Ze in a TT system?
    The black (neutral) is required to power the instrument and in some instances such as DLOC for the electronics to lock the RCD.
     
  7. plugwash

    Joined:
    28 Mar 2004
    Messages:
    8,799
    Thanks Received:
    262
    Country:
    United Kingdom
    Assuming you measure with main bonding disconnected it is the output imedanace of the suppply transformer plus the impedance of your live supply condutor plus the impedance of your electrode plus the impedance of your suppliers electode.

    In practice the impedance of your rod is likely to be much higher than any of the other things mentioned above and it is normal to use the Ze measurement as a conservative estimate of the impedance of your rod.

    testing earth rod resistance seperately requires a different type of tester and several temporary test electrodes but there is rarely any reason to do it.
     
  8. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    Yep, what is the difference between a Ze measured with a 3 wire efli tester and a Ze measured with a 2 wire efli tester?
     
  9. TONY144

    Joined:
    16 Feb 2006
    Messages:
    44
    Thanks Received:
    0
    Location:
    Staffordshire
    Country:
    United Kingdom
    Thanks lads between you all i now have the answer to my initial question.
     