Mixed Radiators and Combi Boiler??!!!!

Joined
9 Mar 2006
Messages
124
Reaction score
0
Location
Kent
Country
United Kingdom
Hello All... Its been a while....
Firstly apologies if this is elsewhere but I cannot find it...
I have a Alpha Combi CD35C boiler and 4 modern radiators, 1 towel rail and an old skool 1 column radiator in my house. I have found the the modern ones loose heat very quickly and towel rail & column maintain their heat. I cant work out if this is good or bad for radiation??!!! Also the modern rads have TRVs except the main one in room with room thermostat/CU.
So I guess my question is how do I set it up so all rads remain warm-hot :eek:
Also are TRV a good or bad idea on that boiler....
Thank you all in advance
 
Sponsored Links
TRV are simply a methoid of controlling the heat in each room while having the heating on for colder rooms. if you close the other valve opposite the TRV on each rad and as you close them, count how many turns it takes on each one to close fully. then open up each one by half the abmmount of turns it took to close. this will restrict the flow rate through the rads. turn all your TRVS to Max and open the rad valve without a TRV full. once your heating is up and toastie check the rads, if too warm turn down valve one turn, if too cold turn up one turn. a bit of playing around should get all rads equal.
 
What the handyman is trying to say is that you need to balance your system, and the info on how to do this is in the FAQs
 