    Hi my boiler is locking out since running out of oil 2days ago -Ive had adelivery today.
    Boiler is danesmann Hatchmoor 12/19
    please can you help as its so freezing here
     
  2. crockett

    Joined:
    15 Mar 2008
    Messages:
    915
    Thanks Received:
    32
    Location:
    Berkshire
    Country:
    United Kingdom
    You need to bleed the oil supply line. This can be done at the pump on the burner. The pump is where the oil line connects to on the burner, if you look at the pump it will have a grub screw located on it, which you can undo slightly to let the air out, catching any oil with a cloth / paper towel. Then try to reignite.
     
  3. leakydave

    Joined:
    2 Nov 2005
    Messages:
    767
    Thanks Received:
    69
    Location:
    Gloucestershire
    Country:
    United Kingdom
    You will need to bleed oil through the oil line. An oil pump wont pump air. Can be messy... wear rubber gloves.

    Isolate oil supply; loosen flexi oil line from burner; open supply and drain oil into suitable container; isolate supply again; reconnect oil line to burner; open oil supply. Reset boiler and cross your fingers. Check for any leaks from the oil line connection.

    Uncontaminated oil can be returned to your oil tank... DON'T tip it down the drain. Dirty oil can be poured onto tissue or newspaper and burnt.
     