Please help! Worcester Bosch 240 problems BG unable to solve

Discussion in 'Plumbing and Central Heating' started by shonky, 3 Jul 2011.

  1. shonky

    Joined:
    3 Jul 2011
    Messages:
    6
    Thanks Received:
    0
    Location:
    Cheshire
    Country:
    United Kingdom
    Hi.
    Im a new member with a problem (my expertise is AV so ill help out as much as I can there!)

    Ive had a Worcester Bosch 240 boiler for nearly 15 years and had it serviced by BG yearly.

    Earlier this year it developed a problem whereas the overheat switch would pop as I filled the bath (usually around 1/3rd full) It would be fine with the central heating or running the shower or sink etc.....The water would alwazs get hot.

    BG were called out to solve the problem and swapped the thermostat cut of sensor plus a couple of other small items.

    After they left the problem was still present so an engineer returned and fitted a new circuit board and adjusted a few settings.....He also added an earthing cable (which incidentally he did not sleeve....naughty!)

    Anyway the problem was still present but I managed to find a way of filling the bath without the overheat tripping ( I would run the bath for a minute or so, stop it for a minute and then repeat..eventually I would get my bath!)

    However now whenever you try and run the hot water it takes an age for the boiler to fire...I mean like 5 minutes.

    You can hear the piezo clicking away but it doesnt fire, after a while it fires and runs hot for a few minutes then goes out.....If left running it tries to ignite and after another few minutes it fires again but soon goes out etc.

    A total nightmare if you are trying to have a shower!

    BG have told me the system needs flushing which will cost over £500 but the engineer didnt seem at all convinced that would cure the problem!

    Any ideas as to what it might be?

    Thanks in anticipation.
     
  2. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    6,949
    Thanks Received:
    877
    Location:
    Glasgow
    Country:
    United Kingdom
    Serviced? in 10 minutes? I do not think so.

    Kick up a stink or get an engineer who can locate and fix the fault instead of taling stabs in the dark
     
  3. nickso

    Joined:
    30 Oct 2006
    Messages:
    6,420
    Thanks Received:
    243
    Country:
    United Kingdom
    how on earth does a flush cure an ignition problem? keep calling them out 'til its fixed.
     
  4. shonky

    Joined:
    3 Jul 2011
    Messages:
    6
    Thanks Received:
    0
    Location:
    Cheshire
    Country:
    United Kingdom
    I know that!.....thats why I declined, they reckon that the heat exchanger gets silted up and that causes the overheat trip to go!

    Ive called them out again for tuesday but im hoping to understand (a little more than they seem to) what the problem might be.
     
  5. nickso

    Joined:
    30 Oct 2006
    Messages:
    6,420
    Thanks Received:
    243
    Country:
    United Kingdom
    sorry, i missed the bit that said the original fault was still present.

    well he is right the DHW heat exchanger can get clogged on these but a flush won't cure it, only stop it happening again. the DHW heat exchanger probably needs replacing, maybe even the primary if the water is bad enough. the O/H stat can also trip if the brass tee piece above the pump is blocked, only seen that on really badly clogged systems though.
     
  6. Jordon

    Joined:
    18 Sep 2008
    Messages:
    614
    Thanks Received:
    95
    Location:
    Bournemouth
    Country:
    United Kingdom
    Sounds like it could be the pump,plate hex or main hex. Need them to test
    it properly.
     
  7. adlplumbing

    Joined:
    9 Dec 2009
    Messages:
    4,509
    Thanks Received:
    381
    Location:
    Lancashire
    Country:
    United Kingdom
    ask them for temp reading on flow and return to heat ex when hot water running
    if heat exchanger is scaled then it temp will rise till over heat kicks in
    if does not then theirs is another problem
     
  8. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    6,949
    Thanks Received:
    877
    Location:
    Glasgow
    Country:
    United Kingdom
    Surely a repair person should not have to be told what to do. When he or she attends a malfunction, what is suggested should automatically have been done to correct the malfunction.
     
  9. shonky

    Joined:
    3 Jul 2011
    Messages:
    6
    Thanks Received:
    0
    Location:
    Cheshire
    Country:
    United Kingdom
    In an ideal world. yes!

    The problem is that it seems like the BG engineers are just stabbing in the dark!

    Im asking here because I want to understand what might be the problem as they spend their hour here and tell me its fixed each time.

    I have an engineer coming tomorrow between 4 and 6 so keep your fingers crossed
     
  10. nickso

    Joined:
    30 Oct 2006
    Messages:
    6,420
    Thanks Received:
    243
    Country:
    United Kingdom
    oh dear, 4-6 is the worst time slot in summer. :LOL:
     
  11. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,396
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    4-6 is hot, they are tired and looking forward to going home.

    Probably as soon as they can get out of your house!
     
  12. breadnbutter

    Joined:
    25 Feb 2011
    Messages:
    1,067
    Thanks Received:
    94
    Location:
    Bedfordshire
    Country:
    United Kingdom
    ipossible hw plate or hw thermister fualt.
     
  13. nickso

    Joined:
    30 Oct 2006
    Messages:
    6,420
    Thanks Received:
    243
    Country:
    United Kingdom
    nope, it's the worst slot 'cos 90% of engineers will be knocked off by 4pm at the moment. that gives you the choice of backshift guys or the weirdo's that do overtime......that in turn means you have higher chance of being bumped after 4pm if the workload is high.
     
  14. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,396
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    I would have thought that there is little overtime being agreed at this quiet time of year.

    A dentist onece told me that he does his best work about 1130 am after he has just had a cup of coffee!

    So I always try to see them at that time!
     
  15. nickso

    Joined:
    30 Oct 2006
    Messages:
    6,420
    Thanks Received:
    243
    Country:
    United Kingdom
    depends on the workload, all you have to do is phone dispatch and ask if they have any work left, if they do your on overtime.

    most days they run out of work at 3pm round here.
     