Potterton Boiler pressure valve leaking water

Discussion in 'Plumbing and Central Heating' started by BunnyBoiler1, 17 Dec 2008.

  1. BunnyBoiler1

    Joined:
    17 Dec 2008
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi - Pressure on combi boiler from sealed system keeps dropping to 0.5bar which means i keep having to open the valve to get it working. When i increase pressure at only one bar the pressure valve of the boiler starts releasing water. What is the likely problem ? This has never happen before - normally i would have to increase the pressure significantly for the pressure valve to release water.
    THanks
    D.
     
  2. swbjackson

    Joined:
    12 Dec 2008
    Messages:
    1,684
    Thanks Received:
    148
    Location:
    Sussex
    Country:
    United Kingdom
    I would suspect that the pressure gauge itself is faulty.

    Mike
     
  3. gavinda

    Joined:
    20 May 2006
    Messages:
    1,241
    Thanks Received:
    26
    Location:
    Berkshire
    Country:
    United Kingdom
    or the prv is just passing and the increase pressure makes it do this more. why not rrelease all prssure cleane the prv valve seat and check the pressure vessel is fully charged.
     
  4. BunnyBoiler1

    Joined:
    17 Dec 2008
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Cheers Guys - Really appreciate your help.

    So if the prv is just passing - i would be supprised due to only 1-1.5 bar of pressure. I would have thought it would take more before it would pass.

    So how do i release all pressure from this potterton puma and how do i clean the prv valve seat ? Is this something a lay person :oops: can do or should I call in specialist help

    Thanks again and Happy Xmas to you both
     