I have a potterton ep2000 programmer with a potterton roomstat.
In the mornings I get Hot water and Central heating but in the evenings I get hot water and warm heating.
It would appear that as long as the hot water is set to on, whenever the tank thermostat is green the pump runs.
If the Central heating is programmed as being on at the same time, it works as long as the hot water is also being heated.
Once the hot water is at temperature the Central heating signal from the room stat does not appear to be good enough to keep the central heating going once the hot water has reached temperature.
If I move the Room Stat off then on a few times, I can hear a clicking noise from either the diverter valve or the pump after 4 or 5 attempts I can sometimes get the pump to start up but not always.
It will then continue to run until the room temperature is met.
Once the room temp is met and then the room cools the pump will not come back on unless I switch the room stat on and off a few times.
In this not working state if ever I move the hot water tank thermostat to a higher temp the pump comes on straight away. (So I don’t think it’s the pump that is at fault)
My immediate reaction is that it’s the room stat is not switching the on signal to the pump at the correct level.
I bought a Drayton 24601bq 3 wire room thermostat from B&Q but still have the same issue.
Are there any tests I can do to isolate where the issue is?
What would you look to replace next?
Any help would be greatly appreciated
Dave
In the mornings I get Hot water and Central heating but in the evenings I get hot water and warm heating.
It would appear that as long as the hot water is set to on, whenever the tank thermostat is green the pump runs.
If the Central heating is programmed as being on at the same time, it works as long as the hot water is also being heated.
Once the hot water is at temperature the Central heating signal from the room stat does not appear to be good enough to keep the central heating going once the hot water has reached temperature.
If I move the Room Stat off then on a few times, I can hear a clicking noise from either the diverter valve or the pump after 4 or 5 attempts I can sometimes get the pump to start up but not always.
It will then continue to run until the room temperature is met.
Once the room temp is met and then the room cools the pump will not come back on unless I switch the room stat on and off a few times.
In this not working state if ever I move the hot water tank thermostat to a higher temp the pump comes on straight away. (So I don’t think it’s the pump that is at fault)
My immediate reaction is that it’s the room stat is not switching the on signal to the pump at the correct level.
I bought a Drayton 24601bq 3 wire room thermostat from B&Q but still have the same issue.
Are there any tests I can do to isolate where the issue is?
What would you look to replace next?
Any help would be greatly appreciated
Dave