    Hi again all i have a potterton performa 24 and the overheat stat keeps clicking out and i have to push the little button in on it to reset. It only happens when the hot water runs but not all the time.

    Anyone help please
     
  2. powell30

    Joined:
    29 Jan 2008
    Messages:
    1,214
    Thanks Received:
    129
    Location:
    Birmingham
    Country:
    United Kingdom
    It's overheating

    Your plate heat ex is most likely sludged or scaled. Clean or replace
     
  3. echoes

    Joined:
    27 Mar 2007
    Messages:
    956
    Thanks Received:
    108
    Location:
    Surrey
    Country:
    United Kingdom
    I had exactly this problem with a similar Potterton. The clips which should hold the thermostats to the return pipe inside had both bust and the stats were just flapping around inside. Worth checking.
     
  4. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,392
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    That last post is not logical !

    If an overheat stat is not in contact it cannot trip because its not being subjected to the heat in the flow pipe.

    The first reply is the one to follow up as its a blocked plate HE.

    Tony
     
  5. echoes

    Joined:
    27 Mar 2007
    Messages:
    956
    Thanks Received:
    108
    Location:
    Surrey
    Country:
    United Kingdom
    The 2 stats not in contact were the control stat on front of boiler and the pump overrun stat. I didn't mention that the overheat stat was attached & functioning (should have done).

    So the only stat functioning was the overheat stat.

    Logical now?

    Sorry for not being clear :oops:
     
  6. okneedhelpplease

    Joined:
    24 Sep 2008
    Messages:
    44
    Thanks Received:
    0
    Location:
    Warwickshire
    Country:
    United Kingdom
    thank you for all the replys, but please tell me, how do i clean the heat exchanger.
    O did i mention it only happens when the hot water is switched off. For example if we shower its fine but when we turn it off it trips
     
  7. petit_pablo

    Joined:
    18 Nov 2007
    Messages:
    7,640
    Thanks Received:
    1,352
    Location:
    Lincolnshire
    Country:
    United Kingdom
    performa doesn't have a pump overrun stat and control stat is connected to board. Thermsistor is screwed into primary flow pipe.
    Are you thinking of profile?
     
    • Thanks Thanks x 1
  8. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,392
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    That is a classic description of a primary heat exchanger which is scaled with lime compounds.

    It can be cleaned in situ with hot sulphonic acid ( DS3 ) but is messy and has to be done by someone who knows what they are doing.

    If it were removed by a gas engineer then it could be cleaned with sulphonic acid or HCl. Again messy and somewhat risky working with acids.

    Not what I would recommend as a DIY job !

    Tony
     
  9. okneedhelpplease

    Joined:
    24 Sep 2008
    Messages:
    44
    Thanks Received:
    0
    Location:
    Warwickshire
    Country:
    United Kingdom
    thank you all
     
  10. echoes

    Joined:
    27 Mar 2007
    Messages:
    956
    Thanks Received:
    108
    Location:
    Surrey
    Country:
    United Kingdom
    Yes petit_pablo, you are spot on - mine was a profile. Thought it was worth a quick post just in case the OP's control stat sensor had become unattached, but thanks for putting me right.
    Good that Potterton ditched the flimsy clips in favour of screws
     
  11. Andygasman2010

    Joined:
    3 Mar 2010
    Messages:
    2,179
    Thanks Received:
    202
    Location:
    Middlesbrough
    Country:
    United Kingdom
    Ahh the confusion! Performa and profile are very different boilers. If it's tripping after the hot water has satisfied then i'd look at the pump overrun facility or the bypass on the system.

    Check that when demand ends the pump continues to run.
     