Rodent Chewed Some outer insulation off 2.5mm Cable

Discussion in 'Electrics UK' started by ahll, 17 Mar 2012.

  1. ahll

    Joined:
    11 Dec 2006
    Messages:
    25
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Hi,
    I have just looked under a kitchen unit where I can see some 2.5mm cable that is feeding a 13A fused Spur. It looks as though some of the insulation has been chewed off in a few places but none of them breaking the coloured insulation on the individual wires.

    What is the best course of action ?

    I believe some people put insulation tape on the affected areas !

    Is heatsrink an option on affected parts ?

    It doesnt seem practical to replace the cable back to the supplying socket as that is in the wall behind the unit and in parts under the tiling.

    There has been no sign of mice since we have had the mice so this probably happened when the house was previously owned.
     
  2. 1john

    Joined:
    3 Oct 2009
    Messages:
    3,351
    Thanks Received:
    341
    Location:
    West Glamorgan
    Country:
    United Kingdom
    I would use self amalgamating tape over insulation tape if thats the option you want to take. Insulation tape will more than likely dry out and fall off over time.
     
  3. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,103
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    Or just SA tape - I can't see any value in putting "insulation" tape under it.
     
  4. conny

    Joined:
    30 Jun 2008
    Messages:
    9,783
    Thanks Received:
    135
    Location:
    Suffolk
    Country:
    United Kingdom
    And for 'future-proofing' after using SA sleeve the exposed cable in plastic conduit. No-one can guarantee you won't have rodents in the future.
     
    • Thanks Thanks x 1
  5. mfarrow

    Joined:
    2 Nov 2009
    Messages:
    1,807
    Thanks Received:
    199
    Location:
    Warwickshire
    Country:
    United Kingdom
    I think 1john probably meant instead of insulation tape.

    If it's to go anywhere, put the insulation tape over the top.
     
  6. mfarrow

    Joined:
    2 Nov 2009
    Messages:
    1,807
    Thanks Received:
    199
    Location:
    Warwickshire
    Country:
    United Kingdom
    Duplicate.
     
  7. 1john

    Joined:
    3 Oct 2009
    Messages:
    3,351
    Thanks Received:
    341
    Location:
    West Glamorgan
    Country:
    United Kingdom
    Indeed, poor choice of vocabulary.
     
    • Thanks Thanks x 1
  8. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,812
    Thanks Received:
    1,237
    Location:
    Oxfordshire
    Country:
    United Kingdom

    You're FIRED!!
     
  9. ahll

    Joined:
    11 Dec 2006
    Messages:
    25
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Just to be clear... you guys are saying its better to use SA tape than heatshrink sheath ?
     
  10. phatboy

    Joined:
    22 Jan 2012
    Messages:
    1,173
    Thanks Received:
    129
    Location:
    Jersey
    Country:
    United Kingdom
    shouldnt make a lot of difference, except that to use heatshrink you will need to disconnect 1 end of the cable to get the thing onto the cable
     
    • Thanks Thanks x 1
  11. plugwash

    Joined:
    28 Mar 2004
    Messages:
    8,818
    Thanks Received:
    265
    Country:
    United Kingdom
    Personally if reasonablly practical to do so i'd say enclosing the cable in conduit would be the best course of action. If rodents have got to the cable before they may do so again.
     
    • Thanks Thanks x 1
  12. ahll

    Joined:
    11 Dec 2006
    Messages:
    25
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    yes I plan to look into using conduit after I have put some protection in the affected bits....
     
  13. 1john

    Joined:
    3 Oct 2009
    Messages:
    3,351
    Thanks Received:
    341
    Location:
    West Glamorgan
    Country:
    United Kingdom
    or nail a steel capping over it.
     
  14. JohnW2

    Joined:
    28 Jan 2011
    Messages:
    24,593
    Thanks Received:
    1,552
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Just noticed this thread. Am I the only person who feels that, before one gets into these discussions about what sort of tape/heatshrink/whatever to use to repair the rodent damage, and what mechanical protection to protect from future rodents, it would be very sensible to undertake an IR test on the cable, and also perhaps others in the vicinity?

    Kind Regards, John.
     
  15. ahll

    Joined:
    11 Dec 2006
    Messages:
    25
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    It will be fully testing so no worries there.
     