Aim replacing a Danfoss RT 230 room stat with a Salus RT 500 programmable digital one

The Salus requires 2 wires

The Danfoss was wired with 3 . These are
Terminal 4 (N) .... Blue
Terminal 1 (com) ....Red
Terminal 2 (on but also sates N) ...... Yellow

The Salus requires me to wire mains live to L and switched live to SL

I am a bit confused by the 3 wires. I assume red will go to L on the new box and yellow to SL, but then what about the blue wire?

Does this blue wire just get made safe and left?

Any help will be appreciated

Thanks
 
Sponsored Links
Your correct , the blue gets isolated and made safe, the other two wires are as you said.
 