Safe distance

Joined
13 Apr 2005
Messages
179
Reaction score
0
Country
United Kingdom
I am currently doing a self build, Elecrician has done 1st fix, but I in my wisdom have moved the washbasin in the bathroom, this may or may not mean I also have to move the shaver socket, can someone please give me a distance it needs to be away, or point me to a Zone diagram if that is what I need.
 
Sponsored Links
How close is it?
300mm from lip of sink to outlet, but will need to check for shaver TFMR.
As its separated there is less hazard, BUT I would still maintain 300mm.
 
Thanks for the prompt reply I may be OK then, I think it is 400mm away from the tap [it is behind and above the basin]
 