Hi,

Would appreciate some advice. Have attempted to replace my thermostat with a different type (Honeywell THR840DUK). The new one whem fitted kept blowing the fuse.

I have re-instated the Satchwell wiring as it was when I removed;

Terminal 1 - Blue
Terminal 3 - Brown
Terminal 4 - Green/Yellow
Back Plate - Bare Earth Wire

When I turn the thermostat up to kick-in the boiler/heathing the fuse keeps blowing.

Any assistance would be much appreciated.

Kind Regards,
 
Sponsored Links
If you have wired it exactly as before then it should be fine. The 2259 is -

Terminal 1 - Switched live
Terminal 3 - Live
Terminal 4 - Neutral

Which, at a guess with your colours would be -

Terminal 1 - Green/Yellow (which is a no no)
Terminal 3 - Brown
Terminal 4 - Blue

Just to stress, this is a guess and the colours could be used any way round. Would need to test with a multimeter to confirm.

The neutral is not required for the new stat.
 