Seperate Oven and Hob
26 Jan 2007
Newcastle upon Tyne
I need to wire a 7.2kw Hob and a 4.5kw Oven and their at opposite sides of the kitchen. Do I need to wire from two individual breakers in my consumer unit and then have a individual isolating switch before each of the appliances. If not how do I get round it and what size cable/ equipment do i need ?
You need a 30A supply for the hob and a 20A supply for the oven.
Cable size will depend on how long the run is, the protective device, how the cable is installed i.e. ambient temp, against thermal insulation, grouped with other cables etc. Also please note that this work will be notifiable to your LABC under part p of the building regs.
You can apply diversity.
You can switch two appliances from the same isolator if they are both within 2m of it.
I have run a 10 mm cooker supply to a cooker 45 amp double pole switch to supply an oven. We were going to have a gas hob adjacent to this but now are going to have a ceramic hob. Can somebody explain if both cooker and hob power supplies can be fitted from the same outlet connection supplied from the switch.
N.B This work is being inspected and tested afterwards as per Part P.
You should start your own thread on this, maybe a mod will do that for you.
But you can wire two appliances from one isolator if they are both within 2m of it.
What loading are the appliances?
It is best to wire a cooker circuit with flc in mind, but it is permissible to apply diversity. Do you know how?