    Just a quick question, when installing a 3 phase balanced motor (no neutral) Is there anyway to do an Earth Fault Loop Impedance test? Or is the only way by calculation after measuring the External loop, and R1R2.
     
  2. Lectrician

    Joined:
    18 Jul 2004
    Messages:
    7,794
    Thanks Received:
    314
    Location:
    Devon
    Country:
    United Kingdom
    If you have a two prong EFL tester, one to live, on to earth.

    If it is a 3 prong tester, put the neutral on the earth, and the earth on the earth, and the live to the live.

    BE AWARE that if the motor is not actually earthed (this is why you are testing), that it will rise to mains voltage when you stick the live on, as the neutral has 'no where' to go.
     
  3. Maxxy

    Joined:
    10 Sep 2006
    Messages:
    390
    Thanks Received:
    1
    Location:
    Essex
    Country:
    United Kingdom
    Thanks for the quick response. The motor is fully earthed, both by the outer sheath, and a cable inside the armoured cable feeding it.

    Its a 3 prong Kewtech tester that ive got. With the method you described, it would be too dangerous, so ill have to stick to calculated readings.

    Thanks again
     
  4. RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    18,414
    Thanks Received:
    1,114
    Location:
    Leeds
    Country:
    United Kingdom
     
  5. Maxxy

    Joined:
    10 Sep 2006
    Messages:
    390
    Thanks Received:
    1
    Location:
    Essex
    Country:
    United Kingdom
    Wouldnt attaching the Neutral and Earth probes to the Earth cable send 230v down the Earth for the duration of the test?

    The motor is part of an industrial fan, so a lot of metal work around it where we fix it to the roof - which i would be kneeling on when doing the test.
     
  6. RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    18,414
    Thanks Received:
    1,114
    Location:
    Leeds
    Country:
    United Kingdom
    Yes the tester will 'send 230V down the earth' but it will onlt be a few mA.

    Providing there is an earth connected to the motor then the metal work will not come live.

    Attaching your tester in this way in no more dangerous that carring out an ELFI test using three test leads.
     
  7. Maxxy

    Joined:
    10 Sep 2006
    Messages:
    390
    Thanks Received:
    1
    Location:
    Essex
    Country:
    United Kingdom
    Brilliant, thanks alot for clearing that up for me
     