Timber stud wall with 30min Fire resistance

Discussion in 'Building' started by rubberneck, 13 Feb 2010.

  1. rubberneck

    Joined:
    16 Apr 2006
    Messages:
    16
    Thanks Received:
    0
    Location:
    Cheshire
    Country:
    United Kingdom
    Hello.
    Can I achieve 30 min fire resistance with a stud wall comprising off 75mm timber and a single layer of 9.5mm plasterboard on each side if the cavity is filled with a rockwool type insulation?

    Any ideas?

    Thanks in advance.
     
  2. Deluks

    Joined:
    23 Feb 2005
    Messages:
    6,788
    Thanks Received:
    328
    Location:
    Surrey
    Country:
    United Kingdom
    Uprate the pb to 12.5mm fireline on both sides and you'll be onto a winner.

    I honestly don't why people would bother wilth 9mm plasterboard in any situation.
     
    • Thanks Thanks x 1
  3. noseall

    Joined:
    2 Feb 2006
    Messages:
    21,749
    Thanks Received:
    1,392
    Location:
    Staffordshire
    Country:
    United Kingdom
    Ditto to the above though fireline board is belt and braces.

    Regular 12.5mm will give you 30mins f.p.
     
    • Thanks Thanks x 1
  4. rubberneck

    Joined:
    16 Apr 2006
    Messages:
    16
    Thanks Received:
    0
    Location:
    Cheshire
    Country:
    United Kingdom
    Thanks for those replies. I've decided to put an additional layer of 9.5mm on either side of the stud wall instead. Hopefully this will aid with sound deadening as well.

    Thanks again.
     
  5. Chukka63

    Joined:
    14 Oct 2009
    Messages:
    903
    Thanks Received:
    81
    Country:
    United Kingdom
    why not just use 1/15mm plasterboard and save on screws and time.
     
  6. PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    18,989
    Thanks Received:
    1,993
    Location:
    Londonderry
    Country:
    United Kingdom
    Double boarding is fine but must agree with the above replys.
    12.5mm plasterboards are the normal these days, 9.5mm not really used that much now by the pro, but it does have a minimum of 30mins fire resistance, whether plastered or unplastered, it's not something I'd recommend though.
     
  7. Master of None

    Joined:
    31 Oct 2007
    Messages:
    400
    Thanks Received:
    16
    Location:
    Edinburgh
    Country:
    United Kingdom
    Also ant penetrations for cables and pipes will need to be dealt with correctly. Ie. fire stop, pipe collars etc.
    Ps not that familiar with domestic situations.
     