    I have electric underfloor heating. has worked well for last 4 years. it uses a Aube TH132 f control module. It appears to be working but the floor isnt heating up. I have repowered the unit after disconnecting for 2 hours. Nothing obviously wrong, but the floor isnt walming up. Any suggestions greatlfully recieved
     
  2. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,668
    Thanks Received:
    1,211
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Do you have a multimeter, or a 2-probe voltage indicator (NOT a neon screwdriver).

    First thing is to check if mains voltage is getting to the input terminals of the controller. If NO then you need to find out why. If YES then...... use the ohms range on your meter and check if the floor element resistance and probe resistance are the same as when the flooring was installed (values should have been written on the instructions).

    If all OK then its likely that the controller is not working.
     
    • Thanks Thanks x 1
  3. ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,347
    Thanks Received:
    383
    Location:
    Gloucestershire
    Country:
    United Kingdom
    To echo TTC's advice above :-

    -Check mains to controller (L+N)
    -Check output from controller. No output when there should be would indicate faulty relay/driver.
    -Check resistance of element 1000w = 53 Ω approx. (other wattages can be worked out from that)
     
    • Thanks Thanks x 1
  4. ericmark

    Joined:
    27 Jan 2008
    Messages:
    8,696
    Thanks Received:
    748
    Location:
    Flintshire
    Country:
    United Kingdom
    I have had problems with my mothers. Normally find fault with thermostat now one her third. I test with a clamp on ammeter as it shows without delay when it starts to work. After the third thermostat went we gave up. Bit hopeless anyway. It takes a good half hour to heat up and once we turn the shower on it's cold again the idea was to dry floor but my mother has finished well before floor is dry.
     
    • Thanks Thanks x 1
  5. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,668
    Thanks Received:
    1,211
    Location:
    Oxfordshire
    Country:
    United Kingdom
    The probe resistance will vary depending on temperature. Expect it to be about 14KΩ at 20°C.
     
    • Thanks Thanks x 1
  6. aic

    aic

    Joined:
    8 Oct 2011
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    many thanks, I will try these tests! :)
     
  7. aic

    aic

    Joined:
    8 Oct 2011
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    have replaced controller, have tested temp sensor. All working. powers on and off ok. But floor still not heating up. resistance of floor element is 13 kohms which i think is ok. so im completely foxed. manual makes reference to possible need of a snubber, which isnt present at present but cant see why this would help with this problem. help!!!!!!!!
     
  8. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,668
    Thanks Received:
    1,211
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Well, I am afraid it isnt.

    Per the above

    How big is the mat? You should be seeing less than 300Ω on the resistance of the floor element.
     
  9. JohnW2

    Joined:
    28 Jan 2011
    Messages:
    23,357
    Thanks Received:
    1,492
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    You don't really mean the element, do you? If you did, 13 kΩ would result in only about 4 watts of heating, which is pretty close to 'not working'!!

    Kind Regards, John.
     
  10. aic

    aic

    Joined:
    8 Oct 2011
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for the information, as you can tell, home electrics isnt my forte/ However i have remeasured across the load part of the circuit it and its about 4 kohms (power off). The heating mat area is 35m2 (large kitchen area). Am I right in thinking that its the element in the floor that isnt working?
     
  11. JohnW2

    Joined:
    28 Jan 2011
    Messages:
    23,357
    Thanks Received:
    1,492
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I'm afraid that's how it's looking.

    Kind Regards, John.
     
    • Thanks Thanks x 1
  12. aic

    aic

    Joined:
    8 Oct 2011
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    thank you all for the information It looks like a very expensive job coming up. I wonder why it stopped working though?
     
  13. JohnW2

    Joined:
    28 Jan 2011
    Messages:
    23,357
    Thanks Received:
    1,492
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Well, it's in the nature of electrical heating elements that they don't last for ever, which is why I would personally be very nervous (to put it lightly) about having any such system. I don't suppose it camne with a 'long-term' warranty, did it?