Hi, my viess. 100 tripped out with an F5 fault.
'I'm not a heating engineer, but have managed to sort out a few breakdowns in the past with the help of this forum and I've read about the air flap valve problem.
However on taking the cover off, it had already been removed, (I recall having a call out under warranty three yrs ago so it must have been done then)
Anyway I turned to the air pressure switch, it has to be that I thought, yes its not making when I blow, then I realised it makes on suction. A check with the meter confirms its working fine. Also checked fan blades were actually turning and not just making a noise.
After much head scratching and calls from the wife to send for the cavalry, I almost gave in, but then I realised I couldnt actually hear the pressure sw operating, so I poked a straw in the air tube spigot on the fan housing and gave it a blow.
Eureka! on re connecting it fired up, so the big question--- was it just dirt
blocking it or is there some form of valve in that area that had stuck?
Anyone else come across this one.
Cheers Ian.
 
Sponsored Links
in spite of the inappropriate advice which has been given by Pete, we do not advise DIYers to even open the combustion chamber and certainly not to interfere with the APS.

Tony
 
Sponsored Links
But it is a pretty crucial safety device that the uninitiated should not be playing with.

Have you heard the phrase "more by luck than judgment"
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Back
Top