Wiring diagram correct for 63A RCCB and 50A MCB?

Discussion in 'Electrics UK' started by Buzzcut, 4 Dec 2009.

  1. Buzzcut

    Joined:
    6 Aug 2004
    Messages:
    12
    Thanks Received:
    0
    Country:
    United Kingdom
    Afternoon...

    I've just bought a new place and scarily there's no RCD on the 10.8 kW electric shower. I had a sparky in to check a few things out and he said to get a standalone 50A 30mA RCD unit that goes next to the CU (rather than replace the whole CU which is a bit old).

    I've got one but would it be bi-directional i.e. can I switch the In with the Out. My feed from the CU is from below but does that still have to be wired into the top of the RCCB as drawn below? Common sense tells me that it can be wired either way but I'm not 100% sure.

    See here for the wiring I'm planning.. http://www.filedump.net/dumped/mcbrccb1259943821.jpg

    Cheers for any advice you can give. I'll get a whole new CU once funds allow but I just want to protect the shower at the mo.

    Buzz
     
  2. Steve

    Joined:
    15 Apr 2005
    Messages:
    16,009
    Thanks Received:
    226
    Location:
    Yorkshire
    Country:
    United Kingdom
    No. Wire it correctly.

    Is your electrician coming back to test this RCD?
     
  3. Buzzcut

    Joined:
    6 Aug 2004
    Messages:
    12
    Thanks Received:
    0
    Country:
    United Kingdom
    ..and correctly would be??

    He'll check it when he wires in the heated floor next week.
     
  4. Steve

    Joined:
    15 Apr 2005
    Messages:
    16,009
    Thanks Received:
    226
    Location:
    Yorkshire
    Country:
    United Kingdom
    Supply in the top of the RCD.

    Shower wired to the N of the RCD bottom, and L of the 50A MCB.
     
  5. Buzzcut

    Joined:
    6 Aug 2004
    Messages:
    12
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks, Steve

    So the drawing was correct only if the supply was coming in the top.

    There's a bar already connecting the L RCD load to the L MCB supply.

    Much appreaciated.

    Buzz
     
  6. flameport

    Joined:
    10 Mar 2007
    Messages:
    4,724
    Thanks Received:
    763
    Location:
    Bournemouth
    Country:
    United Kingdom
    I suggest you get a larger enclosure, that one is barely big enough for the devices and it will be extremely difficult to get 10mm cables in there.
     
  7. ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    52,062
    Thanks Received:
    2,033
    Location:
    London
    Country:
    United Kingdom
    There'd be more space if the pointless MCB were removed.
     
  8. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,800
    Thanks Received:
    1,237
    Location:
    Oxfordshire
    Country:
    United Kingdom
    :?: Do you think that CDL7-63 thingy is an RCBO then?
     
  9. mfarrow

    Joined:
    2 Nov 2009
    Messages:
    1,802
    Thanks Received:
    199
    Location:
    Warwickshire
    Country:
    United Kingdom
    I think BAS was trying to point out that the shower is already fed from the CU - therefore should already be protected by an MCB/fuse.
     