Wireeless Fire Alarm system Components

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Alarms, CCTV & Telephones
Search this topic :: View previous topic :: View next topic  
Author Message
odiadh

from United Kingdom

Joined: 15 Apr 2012
Posts: 3
Location: London,
United Kingdom

PostPosted: Sun Apr 15, 2012 7:16 pm Reply with quote

Hi Guys

I am doing a research for installing a wireless fire alarm system in a BB in London.
The building has 6 floors and 8 rooms in each floor, so it is a good idea to divide it into 8 zones.
would someone please give me a hint of what components should be bought for this system?
1 Central Control unit
48 Detectors (Smoke or heat)
8 Sounders
8 Call Points

any repeaters or something to connect the components through that to the central controller is needed? or the components can connect to the central controller directly?

Cheers
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Europlex

from United Kingdom

Joined: 20 Nov 2007
Posts: 2215
Location: United Kingdom
Thanked: 208 times

PostPosted: Sun Apr 15, 2012 7:47 pm Reply with quote

I know absolutely nothing about fire alarms.

Other than if you need to ask that sort of question about the installation of one in the type of premises you mention, it MUST be done professionally, peoples lives etc, not to mention all the regulations that must be adhered to.

I'm sure 'Alarm' will be along later to point you in the right direction.

Good luck.
Back to top
 Alert Moderators
lee2009

from United Kingdom

Joined: 24 Nov 2008
Posts: 682
Location: Northumberland,
United Kingdom
Thanked: 35 times

PostPosted: Sun Apr 15, 2012 9:33 pm Reply with quote

i know nothing either, but i do lmow id never want a wireless fire system in that big of a property.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Sun Apr 15, 2012 9:33 pm Reply with quote

Start with what your local fire officer and local authority want.
Then with this and wireless get a very large chunk of money ready.
And I mean a very large amount.
Wireless systems of this magnitude are very very expensive. So much so some tend to skimp and use lesser equipment and hope for the best.

8 zones WILL NOT SUFFICE
Smoke or heat WILL NOT SUFFICE , a correct survey is needed and the costs of various detectors will vary a lot.
8 Sounders WILL NOT SUFFICE
8 Call Points WILL NOT EITHER

The above is even without a survey.

To go wireless with this would need a very detailed survey, and then it may not pass. ( Radio survey).


(For the benefit of others Fire Wireless is a lot different to Alarm system wireless due to several factors. People saying anything different have no knowledge).
Back to top
The following user says thank you to Alarm for this useful post:
odiadh (15 Apr 2012)
 Alert Moderators
odiadh

from United Kingdom

Joined: 15 Apr 2012
Posts: 3
Location: London,
United Kingdom

PostPosted: Sun Apr 15, 2012 11:27 pm Reply with quote

This is just to roughly estimate the price of this system.
I found this website that gives me a slight idea of how much the price would be.
http://www.thesafetycentre.co.uk/store/fire_alarm_system_equipment/radio_wireless_fire_alarm_system_equipment/electro_detectors_eda_zerio_plus_wireless_fire_alarm_system_range/

So I just want to know what are the needed components.
The detectors will be just smoke detectors
Back to top
 Alert Moderators
lee2009

from United Kingdom

Joined: 24 Nov 2008
Posts: 682
Location: Northumberland,
United Kingdom
Thanked: 35 times

PostPosted: Sun Apr 15, 2012 11:33 pm Reply with quote

because im interested in all things like this, i belive this applys to you? but i may be wrong and it may be out of date.

"Category L Systems
Category L systems are automatic fire detection systems where the objective is to protect life. Categories are subdivided into the following systems:

L1
This is the highest category for the protection of life and is intended to give the earliest possible notification of a fire in order to allow maximum time for evaluation. Automatic and manual fire detection should be installed throughout all areas of the building with smoke detectors employed wherever possible to protect rooms in which people are expected to be present. All alarm signals given in a category L system must be sufficient to warn people for whom the alarm is intended to allow time for an evacuation.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Sun Apr 15, 2012 11:41 pm Reply with quote

Your missing the point.

You cannot just say " It will be smoke "detectors".
You have to see what is required.
You need sounders at certain points, for particular reasons.
Same as various other items.


You need to get this done correctly.

It looks like your going to try this yourself.

Please please please do not, you will kill someone by error and omission.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Sun Apr 15, 2012 11:46 pm Reply with quote

lee2009 wrote:
because im interested in all things like this, i belive this applys to you? but i may be wrong and it may be out of date.

"Category L Systems
Category L systems are automatic fire detection systems where the objective is to protect life. Categories are subdivided into the following systems:

L1
This is the highest category for the protection of life and is intended to give the earliest possible notification of a fire in order to allow maximum time for evaluation. Automatic and manual fire detection should be installed throughout all areas of the building with smoke detectors employed wherever possible to protect rooms in which people are expected to be present. All alarm signals given in a category L system must be sufficient to warn people for whom the alarm is intended to allow time for an evacuation.



You also missed out a few dozen other items needed to be addressed.
One being smoke detectors are not the only ones to be used.

Easy to quote a reg, another to understand.
Back to top
 Alert Moderators
lee2009

from United Kingdom

Joined: 24 Nov 2008
Posts: 682
Location: Northumberland,
United Kingdom
Thanked: 35 times

PostPosted: Sun Apr 15, 2012 11:49 pm Reply with quote

just trying to show him, what this involves, hopefully he is just trying to get a rough idear of cost and not fit this him self.
Back to top
 Alert Moderators
lee2009

from United Kingdom

Joined: 24 Nov 2008
Posts: 682
Location: Northumberland,
United Kingdom
Thanked: 35 times

PostPosted: Sun Apr 15, 2012 11:58 pm Reply with quote

If the alarm systems is to used in buildings such as hotels, a minimum sound level 75dBA at the bed head is required in order to wake a sleeping person
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Mon Apr 16, 2012 12:01 am Reply with quote

The cost would be irrelevant, it would not be the choice of a professional.
It would not allow for the fitting.

The only panel to be really trusted for this would be 1500 retail.
Not a 400 quid item.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Mon Apr 16, 2012 12:02 am Reply with quote

lee2009 wrote:
If the alarm systems is to used in buildings such as hotels, a minimum sound level 75dBA at the bed head is required in order to wake a sleeping person


Taking into account what?
Plus your figure is wrong.

Stop reading things you have no understanding of.
Back to top
 Alert Moderators
lee2009

from United Kingdom

Joined: 24 Nov 2008
Posts: 682
Location: Northumberland,
United Kingdom
Thanked: 35 times

PostPosted: Mon Apr 16, 2012 12:05 am Reply with quote

my figures are not wrong, this companys may be wrong but my figures are what i gleaned from here:

http://www.bandbelectricalcontractorsltd.co.uk/services/fire-alarm-design.php

fully covered my self here "because im interested in all things like this, i belive this applys to you? but i may be wrong and it may be out of date"

like i say, just trying to show him this is not as simple as he thinks.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Mon Apr 16, 2012 12:15 am Reply with quote

Your figure is incorrect when other factors are used.
However you have also missed something very important in a B&B. Actually a few points.
Ones not covered in that website, give them a call ask them.

Your efforts are worthy, but taking general hints from a website is not knowledge.
Back to top
 Alert Moderators
Alarm

from United Kingdom

Joined: 18 Oct 2010
Posts: 8970
Location: London,
United Kingdom
Thanked: 529 times

PostPosted: Mon Apr 16, 2012 12:21 am Reply with quote

Sorry, I`ll rephrase that.

Gleaning snippets without knowing how and why is not.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Alarms, CCTV & Telephones All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Where is the best place to buy Honeywell alarm components? 2 120 Mon Oct 21, 2013 5:48 pm
Reccomendations for replacement alarm components pls 12 300 Mon Jun 11, 2012 2:26 pm
what type of fire alarm system is required? 7 180 Thu May 31, 2012 9:37 am
Pros and cons of using alarm system for smoke/fire detectors 2 800 Thu Jan 10, 2008 9:59 pm
Can i get local fire station to test my alarm system?? 3 640 Mon Feb 16, 2009 3:12 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.