Replacing an MCB


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
jeffturl

from United Kingdom

Joined: 04 Jul 2009
Posts: 6
Location: Devon,
United Kingdom

PostPosted: Thu Mar 22, 2012 12:23 pm Reply with quote

I am looking to replace the electric shower, the current one is a 8.5kW the new one will be 10.5kW. The current cabling from the shower to the consumer unit is 10mm (i checked before i bought the shower!). The MCB in the consumer unit is rated at 40A. I have picked up a 50A MCB from my local merchants.

My question is about how to safely replace the MCB in the consumer unit. The consumer unit has an RCD switch that covers all MCBs, is it safe to flip the RCD to off and replace the existing 40A MCB with the 50A? or do i need a professional in to safely isolate the consumer unit to carry out this work?

The main fuse before the consumer unit is rated at 80A.

Regards
Jeff
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
scousespark

from United Kingdom

Joined: 18 Jan 2006
Posts: 663
Location: Merseyside,
United Kingdom
Thanked: 32 times

PostPosted: Thu Mar 22, 2012 12:37 pm Reply with quote

The work has to be notified to your LABC.
The safest option you have is to use a Part-P registered electrician.
If you need to ask the questions you have asked, you shouldn't think about doing this yourself.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8427
Location: United Kingdom
Thanked: 197 times

PostPosted: Thu Mar 22, 2012 12:57 pm Reply with quote

jeffturl wrote:
My question is about how to safely replace the MCB in the consumer unit. The consumer unit has an RCD switch that covers all MCBs, is it safe to flip the RCD to off and replace the existing 40A MCB with the 50A?

It SHOULD be if the consumer unit is installed correctly.

However since you don't know whether the consumer unit has been installed correctly you should take extreme care not to touch anything inside when first removing the cover and immediately after removing it you should check for any exposed metal on the incoming connections.

scousespark wrote:
The work has to be notified to your LABC.

It's borderline depending on exactly how narrowly the "replacing fixed equipment" exception is interpreted.
Back to top
 Alert Moderators
Chri5

from United Kingdom

Joined: 19 Jan 2007
Posts: 3991
Location: London,
United Kingdom
Thanked: 341 times

PostPosted: Thu Mar 22, 2012 1:36 pm Reply with quote

The rcd off still means that there is power in to the cu. you should turn off the main switch and turn off the power between main head and cu if you have an in line isolation between the two items.

The mcb should be tested, hence that tends to take the job on to a qualified spark. As for paperwork since the circuit is being upgraded rather than replaced like for like, a cert is required.
Back to top
 Alert Moderators
riveralt

from United Kingdom

Joined: 04 Jan 2004
Posts: 3768
Location: United Kingdom
Thanked: 565 times

PostPosted: Thu Mar 22, 2012 1:56 pm Reply with quote

jeffturl wrote:
I am looking to replace the electric shower, the current one is a 8.5kW the new one will be 10.5kW. The current cabling from the shower to the consumer unit is 10mm (i checked before i bought the shower!). The MCB in the consumer unit is rated at 40A. I have picked up a 50A MCB from my local merchants.
Before you go changing anything have you read the manufacturers instructions regarding the size of the MCB required.
Firstly, the 10.5kw shower will be the headline figure used to sell the product and will be calculated at 240v. The regulations use 230v as the standard figure thus giving the actual rating around 9.6kw. Check your instructions and you will see they give the standard equivalent figure as well.
You have 10mm cable so there is no problem regarding the size of the cable though 6mm T&E would have done.
The purpose of the MCB is to protect the cable and often the manufacturers will require a 40Amp MCB for this size shower.

If they require a larger size MCB then you're back to notifying your Local Authority Building Control in which case it might be cheaper to employ an electriican as previously stated.

As Chris5 said if you turn the RCD off (I assume it incorporates the main switch as well) then the inside of the Consumer will still be live in places and you need to be very careful, especially if the MCB is positioned next the the RCD.
If there is a double pole isolator between the meter and the cu then turn it off here otherwise, be very careful.
Back to top
 Alert Moderators
scousespark

from United Kingdom

Joined: 18 Jan 2006
Posts: 663
Location: Merseyside,
United Kingdom
Thanked: 32 times

PostPosted: Thu Mar 22, 2012 2:01 pm Reply with quote

Granted notifiability is open to interpretation.

However, there is no vagueness when it comes to advising the op to get an electricain in to sort this. I don't think I have ever seen an electrician give advice to open the CU up and 'be careful not to touch anything'.

Have you ever heard of safe isolation?

This was for the benfit of Plugwash.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replacing old socket with round pins 7 421 Tue Sep 21, 2010 6:57 pm
Replacing my shower fan motor problems 4 280 Tue Sep 28, 2010 3:18 pm
Cable route in wall - replacing spur with extended ring 6 280 Thu Sep 30, 2010 9:11 am
Replacing 3 Gang Rocker Switch with 2 Gang Dimmer Switch 6 280 Thu Sep 30, 2010 9:36 am
Replacing section of ring main 10 540 Mon Sep 20, 2010 12:08 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.