Shower Isolation Switch

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Chit

from United Kingdom

Joined: 02 Aug 2011
Posts: 95
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon Mar 26, 2012 10:30 am Reply with quote

Hi all,

I have a Creda Advantage 10.5kw electric shower which is fed by a 10.5mm t&e cable. It is RCD protected and is fed via a 40Amp MCB.

The shower was protected by a 45Amp isolator switch which I have found was bought from wickes:

http://www.wickes.co.uk/invt/204947

A few days ago, I went to switch the isolator on and got nothing from it. I checked the MCB and RCD and both were switched on.

On testing the isolator, I was getting 230V at the supply side of the switch. On switching the isolator on though, nothing was being given on the load side of the isolator.

I bought a new isolator switch and on opening the old one up again, I noticed that the plastic sheathing on the load live cable was black and crumbly. I cut and stripped this back until I got to untarred copper.

My question is why would this happen? I'm guessing the the cable had not been stripped back far enough by the electrician who fitted it and it was touching the copper internals of the isolator switch. When the current was flowing and the cable was hot, I'm guessing that this had burnt the sheathing?

I also remember that when the electrician was fitting the isolator, I did ask if it should be of a higher amperage as the max current flowing may hit 45.6 Amps but he explained that the mcb would cut the current before the isolator was affected and so it was fine. - Is it fine or should the isolator be of a higher amperage?

Many thanks.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Mon Mar 26, 2012 11:14 am Reply with quote

..


Last edited by holmslaw on Thu Apr 12, 2012 8:39 am, edited 1 time in total
Back to top
 Alert Moderators
Chit

from United Kingdom

Joined: 02 Aug 2011
Posts: 95
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon Mar 26, 2012 1:26 pm Reply with quote

Hi, many thanks for that. When un doing the connections, none were even slightly loose to be really honest, all were sufficiently tight?

Also, the way the electrician advised me, only a maximum of 45Amps will reach the isolator as that's the maximum allowed through the MCB. For this reason, the isolator will be protected by the MCB and therefore should be fine? Is this true?

Could it even have simply been a faulty switch ?
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25198
Location: Cheshire,
United Kingdom
Thanked: 441 times

PostPosted: Mon Mar 26, 2012 3:10 pm Reply with quote

holmslaw wrote:
I would fit a 50A + isolator switch.


And a 50A MCB.
Back to top
 Alert Moderators
sparkwright

from United Kingdom

Joined: 20 Aug 2009
Posts: 4198
Location: Dorset,
United Kingdom
Thanked: 520 times

PostPosted: Mon Mar 26, 2012 5:23 pm Reply with quote

securespark wrote:
holmslaw wrote:
I would fit a 50A + isolator switch.


And a 50A MCB.


Not too sure on the cable size yet. 10.5 mm has been mentioned, so there may be some confusion in determining the cable size.
Back to top
 Alert Moderators
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 1071
Location: United Kingdom
Thanked: 39 times

PostPosted: Mon Mar 26, 2012 6:59 pm Reply with quote

Pullcord type shower switches are rubbish in my opinion, a better solution is to use a main switch type of assembly (63amp) in a two width din rail box, in the airing cupboard outside the bathroom. icon_lol.gif icon_lol.gif icon_lol.gif

The pull cord switches tend to fail on a regular basis, from reading other posts on this site over several years, and do not seem man enough for the job. icon_lol.gif icon_lol.gif icon_lol.gif
Back to top
 Alert Moderators
EFLImpudence

from United Kingdom

Joined: 07 Jul 2010
Posts: 9161
Location: Dorset,
United Kingdom
Thanked: 1081 times

PostPosted: Mon Mar 26, 2012 9:08 pm Reply with quote

Chit wrote:
only a maximum of 45Amps will reach the isolator as that's the maximum allowed through the MCB.

Not true.
Back to top
 Alert Moderators
Chit

from United Kingdom

Joined: 02 Aug 2011
Posts: 95
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon Mar 26, 2012 10:21 pm Reply with quote

Sorry guys, have been in a rush all day and so typed a load of incorrect facts....

Firstly, the cable is 10mm t&e.
Secondly, the electrician said that only a max of 40Amps will reach the isolator as the MCB is rated at 40Amps.
Back to top
 Alert Moderators
Chit

from United Kingdom

Joined: 02 Aug 2011
Posts: 95
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon Mar 26, 2012 10:22 pm Reply with quote

kai wrote:
Pullcord type shower switches are rubbish in my opinion, a better solution is to use a main switch type of assembly (63amp) in a two width din rail box, in the airing cupboard outside the bathroom. icon_lol.gif icon_lol.gif icon_lol.gif

The pull cord switches tend to fail on a regular basis, from reading other posts on this site over several years, and do not seem man enough for the job. icon_lol.gif icon_lol.gif icon_lol.gif


Thanks for that, do you have any links for these switches?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14258
Location: Cumbria,
United Kingdom
Thanked: 409 times

PostPosted: Mon Mar 26, 2012 10:34 pm Reply with quote

Chit wrote:

Secondly, the electrician said that only a max of 40Amps will reach the isolator as the MCB is rated at 40Amps.


Rubbish, in simplistic terms the current is caused by the resistance of the load and the supply voltage.
A 10.5KW shower pulls around 44A @ 240v.
Isolators do wear out resulting in them heating up.
A 40A MCB does not trip at 40A, nor does it limit the supply current. It is a poor design to have a 40A MCB supplying a load of 40A> though.
Back to top
 Alert Moderators
EFLImpudence

from United Kingdom

Joined: 07 Jul 2010
Posts: 9161
Location: Dorset,
United Kingdom
Thanked: 1081 times

PostPosted: Mon Mar 26, 2012 10:45 pm Reply with quote

Back to top
 Alert Moderators
Chit

from United Kingdom

Joined: 02 Aug 2011
Posts: 95
Location: United Kingdom
Thanked: 1 time

PostPosted: Tue Mar 27, 2012 7:26 am Reply with quote

Spark123 wrote:
Chit wrote:

Secondly, the electrician said that only a max of 40Amps will reach the isolator as the MCB is rated at 40Amps.


Rubbish, in simplistic terms the current is caused by the resistance of the load and the supply voltage.
A 10.5KW shower pulls around 44A @ 240v.
Isolators do wear out resulting in them heating up.
A 40A MCB does not trip at 40A, nor does it limit the supply current. It is a poor design to have a 40A MCB supplying a load of 40A> though.


Really? This is exactly how the spark who installed the circuit advised me, sometimes I really wonder who to trust, you employ someone to do a job for you and they simply can't be bothered to do it properly and lie to you.... Is it dangerous? Do you get 50Amp Isolator switches?(not the pull cord type, I need a rocker switch type) - not been able to find any in local shops etc?

Also, what is the theory behind this so that I know for the future? How much current is allowed to pass through a 40Amp MCB? What would the MCB if not limit the supply ?
Back to top
 Alert Moderators
EFLImpudence

from United Kingdom

Joined: 07 Jul 2010
Posts: 9161
Location: Dorset,
United Kingdom
Thanked: 1081 times

PostPosted: Tue Mar 27, 2012 3:26 pm Reply with quote

A 'B type' MCB will pass 1.13 times its rating (40 x 1.13 = 45.2A) 'for ever'.

Probably what he was thinking of when he told you but with the wrong conclusion.

At 1.45 times its rating (40 x 1.45 = 58A) it will take an hour to trip.

Getting progressively quicker until ...

it should trip 'instantly' with a current of 5 times its rating (40 x 5 = 200A) but that would likely be a short-circuit of much greater amperage.
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Tue Mar 27, 2012 6:41 pm Reply with quote

..


Last edited by holmslaw on Thu Apr 12, 2012 8:40 am, edited 1 time in total
Back to top
 Alert Moderators
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 1071
Location: United Kingdom
Thanked: 39 times

PostPosted: Tue Mar 27, 2012 7:37 pm Reply with quote

Chit wrote:
Thanks for that, do you have any links for these switches?


It is just a standard consumer unit format main switch, sold at B&Q and similar places, mounted in a 2 slot din-mount box or enclosure, also sold at B&Q etc.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shower isolation switch 18 240 Sun Nov 17, 2013 1:45 pm
Replaced shower, and isolation switch. Rcd trips 23 6300 Thu Mar 13, 2008 11:34 pm
shower isolation switch location 12 1640 Sun Jun 19, 2011 7:19 pm
Overheating N cable in shower Isolation Switch 7 180 Fri Feb 21, 2014 10:12 pm
Electric shower isolation switch? 2 380 Fri Nov 13, 2009 9:44 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.