Is it OK to wire a spur consisting of a radial (2.5mm T & E cable) to two adjacent SFU's for a 10amp supply on one of the SFU's and a 2amp supply on the other SFU.
Not really, IMO, since there's no guarantee that someone won't come along in the future and put 13A fuses in both SFCUs and connect both to high loads - it would therefore be advisable for each SFCU to have its own separate 2.5mm² feed from the ring. Others may disagree, on the (true) basis that the present situation (with 10A and 2A fuses) would not be a problem.Is it OK to wire a spur consisting of a radial (2.5mm T & E cable) to two adjacent SFU's for a 10amp supply on one of the SFU's and a 2amp supply on the other SFU.
Very true, but the MIs of whatever is on the end of the '2A supply' might be demanding something smaller than a 13A fuse.If you use just one FCU (13A) and used 1.0mm² cable to both items you wouldn't need a 2A fuse.
Agreed.Yes, might do but the circuit will comply whatever else is put on it.
Possibly - hopefully the OP will clarify. I was thinking that maybe there was one load who's MIs were calling for a 2A or 3A fuse and that the OP, thinking that the whole spur should be limited to 13A max, therefore decided on 10A for the other FCU. Hopefully we'll get some more information.What do you think would require (by the manufacturer) a 10A and 2A fuse? I was imagining a 2A socket being fitted and a misunderstanding of the meaning.
If that's what was meant, it would obvioulsy be fine - but that's not how I read it (I assumed he meant just two FCUs fed from the same connection to the ring). As I've just written, we need some clarification.Unless I'm reading it wrong, the plan is to have one FCU supplying two further FCU's in a radial.
I agree with John as far as the number of FCUs proposed.Unless I'm reading it wrong, the plan is to have one FCU supplying two further FCU's in a radial.
Is it OK to wire a spur consisting of a radial (2.5mm T & E cable) to two adjacent SFU's for a 10amp supply on one of the SFU's and a 2amp supply on the other SFU.
That doesn't alter my interpretation (perhaps wrong!) of what the OP wrote. I thought, and still think, that 'radial' was used to describe a single cable spurred from the ring and feeding the supply side of two FCUs. Only the OP can clarify.Ah 'ring' in heading and 'radial' (missed) in post.
HI John you are right in your assumption of a spur off the ring to two FCU's As I thought that it was ok to spur a double socket off the ring it would be ok to spur two FCU's as both senarios are capable of supplying two 13amp loads in total (although I am only supplying a total load of 12 amps) I would appreciate your thoughts on this. (wildman147)That doesn't alter my interpretation (perhaps wrong!) of what the OP wrote. I thought, and still think, that 'radial' was used to describe a single cable spurred from the ring and feeding the supply side of two FCUs. Only the OP can clarify.Ah 'ring' in heading and 'radial' (missed) in post.
Kind Regards, John
Ah, my thoughts The regulations are not necessarily very logical/consistent about this since, although (as you say) they allow a double socket on an unfused spur, they do not allow two single sockets (or, indeed, two 'of anything' - which includes your situation). Don't ask me to explain/justify that, beyond the fact that, contrary to common beliefs, double sockets are not designed to be able to cope with 2 x 13A loads - 20A (not 26A) is usually regarded as the maximum, with the instructions of some seemingly implying that the acceptable total is only 13A (across both socket outlets).HI John you are right in your assumption of a spur off the ring to two FCU's As I thought that it was ok to spur a double socket off the ring it would be ok to spur two FCU's as both senarios are capable of supplying two 13amp loads in total (although I am only supplying a total load of 12 amps) I would appreciate your thoughts on this. (wildman147)