Underfloor heating has stopped working


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
aic

from Unknown or unspecified country

Joined: 08 Oct 2011
Posts: 6
Location: Unknown or unspecified country

PostPosted: Sat Oct 08, 2011 2:07 pm Reply with quote

I have electric underfloor heating. has worked well for last 4 years. it uses a Aube TH132 f control module. It appears to be working but the floor isnt heating up. I have repowered the unit after disconnecting for 2 hours. Nothing obviously wrong, but the floor isnt walming up. Any suggestions greatlfully recieved
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12616
Location: Oxfordshire,
United Kingdom
Thanked: 1050 times

PostPosted: Sat Oct 08, 2011 2:25 pm Reply with quote

Do you have a multimeter, or a 2-probe voltage indicator (NOT a neon screwdriver).

First thing is to check if mains voltage is getting to the input terminals of the controller. If NO then you need to find out why. If YES then...... use the ohms range on your meter and check if the floor element resistance and probe resistance are the same as when the flooring was installed (values should have been written on the instructions).

If all OK then its likely that the controller is not working.
Back to top
The following user says thank you to Taylortwocities for this useful post:
aic (8 Oct 2011)
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 6308
Location: Gloucestershire,
United Kingdom
Thanked: 377 times

PostPosted: Sat Oct 08, 2011 2:39 pm Reply with quote

To echo TTC's advice above :-

-Check mains to controller (L+N)
-Check output from controller. No output when there should be would indicate faulty relay/driver.
-Check resistance of element 1000w = 53 Ω approx. (other wattages can be worked out from that)
Back to top
The following user says thank you to ricicle for this useful post:
aic (8 Oct 2011)
 Alert Moderators
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 7818
Location: Flintshire,
United Kingdom
Thanked: 663 times

PostPosted: Sat Oct 08, 2011 3:01 pm Reply with quote

I have had problems with my mothers. Normally find fault with thermostat now one her third. I test with a clamp on ammeter as it shows without delay when it starts to work. After the third thermostat went we gave up. Bit hopeless anyway. It takes a good half hour to heat up and once we turn the shower on it's cold again the idea was to dry floor but my mother has finished well before floor is dry.
Back to top
The following user says thank you to ericmark for this useful post:
aic (8 Oct 2011)
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12616
Location: Oxfordshire,
United Kingdom
Thanked: 1050 times

PostPosted: Sat Oct 08, 2011 3:47 pm Reply with quote

ricicle wrote:
To echo TTC's advice above :-

-Check mains to controller (L+N)
-Check output from controller. No output when there should be would indicate faulty relay/driver.
-Check resistance of element 1000w = 53 Ω approx. (other wattages can be worked out from that)


The probe resistance will vary depending on temperature. Expect it to be about 14KΩ at 20C.
Back to top
The following user says thank you to Taylortwocities for this useful post:
aic (8 Oct 2011)
 Alert Moderators
aic

from Unknown or unspecified country

Joined: 08 Oct 2011
Posts: 6
Location: Unknown or unspecified country

PostPosted: Sat Oct 08, 2011 5:12 pm Reply with quote

many thanks, I will try these tests! icon_smile.gif
Back to top
 Alert Moderators
aic

from Unknown or unspecified country

Joined: 08 Oct 2011
Posts: 6
Location: Unknown or unspecified country

PostPosted: Sat Oct 15, 2011 4:38 pm Reply with quote

have replaced controller, have tested temp sensor. All working. powers on and off ok. But floor still not heating up. resistance of floor element is 13 kohms which i think is ok. so im completely foxed. manual makes reference to possible need of a snubber, which isnt present at present but cant see why this would help with this problem. help!!!!!!!!
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12616
Location: Oxfordshire,
United Kingdom
Thanked: 1050 times

PostPosted: Sat Oct 15, 2011 4:47 pm Reply with quote

Quote:
resistance of floor element is 13 kohms which i think is ok


Well, I am afraid it isnt.

Per the above

ricicle wrote:

-Check resistance of element 1000w = 53 Ω approx. (other wattages can be worked out from that)


How big is the mat? You should be seeing less than 300Ω on the resistance of the floor element.
Back to top
 Alert Moderators
JohnW2

from United Kingdom

Joined: 28 Jan 2011
Posts: 18787
Location: Buckinghamshire,
United Kingdom
Thanked: 1171 times

PostPosted: Sat Oct 15, 2011 4:50 pm Reply with quote

aic wrote:
.... But floor still not heating up. resistance of floor element is 13 kohms which i think is ok....

You don't really mean the element, do you? If you did, 13 kΩ would result in only about 4 watts of heating, which is pretty close to 'not working'!!

Kind Regards, John.
Back to top
 Alert Moderators
aic

from Unknown or unspecified country

Joined: 08 Oct 2011
Posts: 6
Location: Unknown or unspecified country

PostPosted: Sat Oct 15, 2011 6:56 pm Reply with quote

Thanks for the information, as you can tell, home electrics isnt my forte/ However i have remeasured across the load part of the circuit it and its about 4 kohms (power off). The heating mat area is 35m2 (large kitchen area). Am I right in thinking that its the element in the floor that isnt working?
Back to top
 Alert Moderators
JohnW2

from United Kingdom

Joined: 28 Jan 2011
Posts: 18787
Location: Buckinghamshire,
United Kingdom
Thanked: 1171 times

PostPosted: Sat Oct 15, 2011 7:30 pm Reply with quote

aic wrote:
Thanks for the information, as you can tell, home electrics isnt my forte/ However i have remeasured across the load part of the circuit it and its about 4 kohms (power off). The heating mat area is 35m2 (large kitchen area). Am I right in thinking that its the element in the floor that isnt working?

I'm afraid that's how it's looking.

Kind Regards, John.
Back to top
The following user says thank you to JohnW2 for this useful post:
aic (15 Oct 2011)
 Alert Moderators
aic

from Unknown or unspecified country

Joined: 08 Oct 2011
Posts: 6
Location: Unknown or unspecified country

PostPosted: Sat Oct 15, 2011 7:41 pm Reply with quote

thank you all for the information It looks like a very expensive job coming up. I wonder why it stopped working though?
Back to top
 Alert Moderators
JohnW2

from United Kingdom

Joined: 28 Jan 2011
Posts: 18787
Location: Buckinghamshire,
United Kingdom
Thanked: 1171 times

PostPosted: Sat Oct 15, 2011 7:47 pm Reply with quote

aic wrote:
thank you all for the information It looks like a very expensive job coming up. I wonder why it stopped working though?

Well, it's in the nature of electrical heating elements that they don't last for ever, which is why I would personally be very nervous (to put it lightly) about having any such system. I don't suppose it camne with a 'long-term' warranty, did it?

Kind Regards, John.
Back to top
 Alert Moderators
Moderator 11
Moderator Comment
Posted: Sun Oct 16, 2011 9:17 am    Comment:

Please note rule 5 (Please do not duplicate your posts.) - See here for the forum rules.
-
I will remove the other one
 
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shower stopped working. 11 520 Thu Jul 29, 2010 11:13 am
socket stopped working, why? 12 880 Sat Feb 27, 2010 4:47 pm
Kitchen lights stopped working - please help! 4 320 Mon Oct 11, 2010 4:25 pm
Table Lamp Stopped Working 3 240 Fri Oct 22, 2010 5:34 pm
Half my sockets in lounge just stopped working! Please help! 15 480 Sun Oct 24, 2010 2:15 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.