baxi boiler pressure gauge problem.


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
32tybeams

from United Kingdom

Joined: 18 Oct 2011
Posts: 13
Location: United Kingdom

PostPosted: Tue Oct 18, 2011 4:26 pm Reply with quote

I have a baxi combi 80e boiler. I'm finding that every morning i have to check the pressure gauge. The needle always seems to drop to 0.5. Being in fear of it droping to under that. I then refill using the filling loop Only reilling upto 1 notch above: 0.5. Then a few hours later when i switch heating on ( the needle being in the same place as was after refilling earlier) the needle gradually goes up to 3. Then gradually drops down to where it should be normally. Anybody have any idea why this is happening? And what i should do about it?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
misterdubya

from United Kingdom

Joined: 02 Oct 2010
Posts: 2873
Location: United Kingdom
Thanked: 293 times

PostPosted: Tue Oct 18, 2011 4:50 pm Reply with quote

Look up FAQ's.

Expansion Vessel flat or knackered.
Back to top
The following user says thank you to misterdubya for this useful post:
32tybeams (20 Oct 2011)
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2286
Location: Manchester,
United Kingdom
Thanked: 128 times

PostPosted: Tue Oct 18, 2011 5:14 pm Reply with quote

When water gets heated it expands in volume. The extra water has to be accommodated using an expansion vessel. The vessel has a flexible diaphragm which is initially held to one side by inflating the other side with air
In operation the heated water will push against the diaphragm and compress the 'air' which will be released again when water cools down.
It is suggested that over time the initial 'air' pressure has been lost or greatly reduced. This has resulted in too small a volume for the extra water and in turn the water pressure rises. There is a relief valve set to open and discharge water at 3bar pressure and when it does this the 3bar pressure is released and the PRV quickly closes again leaving a pressure of 0.5bar
Sometime the PRV does not close properly, because of dirt on the seating face and it may have to be changed. It is important however to deal with the expansion vessel first.
There is also a possibility the diaphragm in the expansion vessel is ruptured which would allow water to pass across to the 'air' side.
Back to top
 Alert Moderators
32tybeams

from United Kingdom

Joined: 18 Oct 2011
Posts: 13
Location: United Kingdom

PostPosted: Thu Oct 20, 2011 5:46 pm Reply with quote

Thanks to your response. I'm getting the idea of problem now through reading and rereading it a few times as well as looking at the manual and identifying the mentioned parts. you seem to be very clued up about it. I will shop around and try to get a reasonable quote for inspection, repair or replace of the extention vessel and prv. I don't suppose you would have any idea what the cost is likely to be? Thanks again for being so helpful.
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2286
Location: Manchester,
United Kingdom
Thanked: 128 times

PostPosted: Thu Oct 20, 2011 6:31 pm Reply with quote

I suggest you read the problem of 'AndyMcG' who has just resolved a similar type problem without bring in a heating engineer.
From what I recall I think PRVs will be around the 15 mark and expansion vessels obvious vary according to size and make, I think I've seen some at 'Toolstation' around the 30 mark.
However I think your problem is another case of the vessel losing air which results in the water pressure increasing to a unacceptable figure and opening the PRV.
If you have a 'air pressure gauge' and bicycle/ car foot pump and follow the correct procedure you could do it yourself
Back to top
The following user says thank you to MANDATE for this useful post:
32tybeams (20 Oct 2011)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Baxi 80e/105e pressure gauge going up on HW demand 2 60 Mon Feb 14, 2011 1:42 pm
Vaillant 828E TurboMax Combi Boiler Pressure Gauge Problem 8 140 Sun Jan 27, 2013 8:09 pm
Worcester 24Cdi Pressure gauge problem 7 840 Sun May 21, 2006 11:01 am
Ideal Classic Boiler LXFF25O - Pressure Gauge 5 260 Sun Sep 12, 2010 7:40 pm
Can someone explain pressure gauge on combi-boiler? 5 4200 Fri Sep 16, 2005 10:13 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.