PostPosted: Wed Apr 25, 2012 1:55 pm Reply with quote

I have an external grant boiler which was installed in August 2007 along with a complete re plumb of the entire house. From the beginning the system was noisy but I was advised that this was because it was new and things would settle down once all the air was out of the system.

After 18 months I started to have real problems: boiler not firing, pressure dropping, some days no hot water. I have the boiler services regularly, have had the oil tank drained and cleaned and pipe work flushed through. At Christmas the boiler stopped and had a couple of valves including the PRV changed along with the jets and filter plus a lamp and switch. Since then my plumber and boiler engineer have been out 6 times, the most recent being last weekend. The pressure release valve is leaking again and once again needs replacing.

I really had hoped that by installing a new boiler i would have some hassle free years without huge bills and not be looking at replacing it in under 5 years of installation. Looking online it appears a number of other people have had issues with these external boilers losing pressure.

Can anyone one please give any advice as I really don't understand boilers and as a single recently unemployed mum of two could do without paying out hundreds of pounds in a regular basis just to keep this boiler firing?

Would appreciate any advice or knowledge that anyone could share.

Helen
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 11267
Location: Northumberland,
United Kingdom
Thanked: 2284 times

PostPosted: Wed Apr 25, 2012 2:02 pm Reply with quote

Really the first thing to achieve is a stable water pressure inside the boiler, which is often between 1 and 1.5 bar.
This pressure should rise a little when the heating is on, but it should return down again when off.
If the pressure rises a lot, then its likely that the expansion vessel inside the boiler needs recharging with air.
Its true, PRV's can be notorious for not sealing once opened, but they should only open at 3 bar anyway so - is the filling loop shut off, or ideally disconnected? Whats the pressure on the gauge?
John icon_smile.gif
Back to top
 Alert Moderators
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3330
Location: Humberside,
United Kingdom
Thanked: 502 times

PostPosted: Wed Apr 25, 2012 7:16 pm Reply with quote

Most likely expansion vessel is simply out of air.

Your plumber sounds hopeless.

I have installed gas and oil central heating systems
and they have years of trouble free running.

Get someone else in.
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4871
Location: Suffolk,
United Kingdom
Thanked: 902 times

PostPosted: Wed Apr 25, 2012 8:25 pm Reply with quote

On the Grant or any other boiler that uses a braided flexible pipe to connect the vessel to the system it is important to check that the flexi hose is not blocked - I have seen this numerous times !
Back to top
The following user says thank you to Boilerman2 for this useful post:
DeltaT2 (26 Apr 2012)
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 5051
Location: Cornwall,
United Kingdom
Thanked: 777 times

PostPosted: Wed Apr 25, 2012 10:27 pm Reply with quote

boilerman 2 has the right idea. when grant boilers are serviced etc. to get to the baffles the pressure vessel. has to be out of the way. if the vessel isn't placed right then the braided hose can very easily be kinked. add that to a large system. hey presto. the prvs on grant external are around 2.5 bar release rather than the 3 bar norm . i keep a few in stock as it is a common problem they let by. but thats mostly due to incompetent installation. e.g no flushing as it seems people think an oil boiler can be installed on a dirty system. bad servicing e.g not checking the vessel. or just basic incompetence.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52428
Location: London,
United Kingdom
Thanked: 3285 times

PostPosted: Wed Apr 25, 2012 10:50 pm Reply with quote

You do seem to have had a pretty poor installation which was compounded by an inability to sort out the problems.

Perhaps you are seen as a "soft touch" ?

Tony
Back to top
 Alert Moderators
Helendav

from United Kingdom

Joined: 23 Apr 2012
Posts: 2
Location: Sussex,
United Kingdom

PostPosted: Thu Apr 26, 2012 6:38 am Reply with quote

John, the pressure is set to 1 bar currently but as the plumber located this along with the cylinder in a hard to access roof space I cannot keep an eye on it easily! The filling loop is turned off.

Thanks guys for your comments, nobody has mentioned the potential flexible hose issue before so will check that out.

Hotly, the pressure release valve that is on there is 2.5 bar, should it be 3? The expansion vessel is 12l and 3 bar.

Not sure if it's relevant but I am running 17 radiators off this system which are the AVOCA type that look like old fashioned school radiators.

As for being a soft touch, perhaps I was when I started this project 5 years ago but I've changed a lot and nobody gets one over on me any more!

Thank you for all your help and suggestions.

Helen icon_smile.gif
Back to top
 Alert Moderators
DeltaT2

from United Kingdom

Joined: 24 Aug 2011
Posts: 1401
Location: Glasgow,
United Kingdom
Thanked: 165 times

PostPosted: Thu Apr 26, 2012 7:45 am Reply with quote

Boilerman2 wrote:
On the Grant or any other boiler that uses a braided flexible pipe to connect the vessel to the system it is important to check that the flexi hose is not blocked - I have seen this numerous times !


A very good point BM & as always you're right on the money.......... icon_wink.gif

The hard of thinking CC/CCC, would learn so much from simply reading your threads & posts BM, people like you are highly valued members here, you know your onions mate.
Thanks BM
Back to top
 Alert Moderators
Burnerman

from United Kingdom

Joined: 07 Feb 2008
Posts: 11267
Location: Northumberland,
United Kingdom
Thanked: 2284 times

PostPosted: Thu Apr 26, 2012 8:03 am Reply with quote

The braided flexy on these does have a very tight bend anyway, if I recall icon_exclaim.gif
Just for info Helen, the round red expansion vessel should be pre charged with air at 1 bar......thats with the flexy pipe disconnected.
John icon_smile.gif
Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4871
Location: Suffolk,
United Kingdom
Thanked: 902 times

PostPosted: Thu Apr 26, 2012 7:33 pm Reply with quote

And with that number of Column Radiators fitted, the on-board expansion vessel (12 litre) may be too small for the water content, an additional expansion vessel may need to be fitted on the cool part of the system on the CH return pipe (Grant fit the largest vessel that will fit into the boiler case - it is not always big enough!) icon_wink.gif
Back to top
 Alert Moderators
holty

from United Kingdom

Joined: 14 Jan 2006
Posts: 5051
Location: Cornwall,
United Kingdom
Thanked: 777 times

PostPosted: Thu Apr 26, 2012 8:13 pm Reply with quote

Quote:
And with that number of Column Radiators fitted, the on-board expansion vessel (12 litre) may be too small for the water content, an additional expansion vessel may need to be fitted on the cool part of the system on the CH return pipe (Grant fit the largest vessel that will fit into the boiler case - it is not always big enough!)


i think without looking. even grant literature will state that.
Back to top
 Alert Moderators
snb

from United Kingdom

Joined: 10 Oct 2007
Posts: 1513
Location: Norfolk,
United Kingdom
Thanked: 227 times

PostPosted: Thu Apr 26, 2012 8:18 pm Reply with quote

same as others stated.

With 17 old style rads i would say the standard 12lt pressure vessel to be too small. Get them to fit an additional vessel on the loft and this should solve the problem
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52428
Location: London,
United Kingdom
Thanked: 3285 times

PostPosted: Sat Apr 28, 2012 1:35 pm Reply with quote

Better to see if its adequate by watching the pressure increase from 1.5 Bar colt to see what it is when hot. It should still be less than 2.0 Bar.

But it some rads have air at the top this will also absorb expansion so dont go round bleeding then just for the sake of it as that will compound the situation.

Tony
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Grant Vortex Condensing Combi 26 hot water problems 30 7000 Sat Feb 19, 2011 3:45 pm
grant vortex pro condensing boiler cutting out 14 220 Fri Dec 28, 2012 12:34 pm
Grant Vortex Pro External Electronic Condensing Combi 21kw 4 480 Tue Nov 03, 2009 11:18 pm
Grant Vortex Condensing Combi 26 - no hot water 16 320 Sat Jul 12, 2014 6:41 am
Grant Vortex Condensing combi 26 - pressure gauge help 4 140 Thu Jul 10, 2014 10:13 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.