How to unblock 10mm flow pipes?


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Mon Oct 22, 2012 9:27 pm Reply with quote

Hi, I've had an ongoing problem with 4 upstairs radiators not getting as hot as they should. They do get warm along the top but the bottom is always cold, the return pipe tends to be hot but the flow pipe is cold so I assume it is heating via convection rather than flow?

I've tried isolating single radiators, changing the pump and even powerflushing but nothing has helped.

Recently I tested the the flow from the pipes into a bucket. The return seemed ok but the flow pipe barely dribbled. I tried draining down, removing the TRV and and attaching a small pump to the pipe but there was resistance stopping the pump.

I guess the pipe are truly blocked?

The system is open vented with with 18 radiators piped with 10mm plastic (with 10mm copper to downstairs). The boiler is a Trianco Oil and I do have a Magnaclean fitted.

I'm thinking about draining the system and injecting a small amount of DS40 directly into one of the blocked legs to see if this will clear the blockage.

Is this safe to do and will it help or is there better things to try first?

Thanks in advance.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Mon Oct 22, 2012 10:03 pm Reply with quote

how do you know that the flow is cold & the ret hot ? i would say it's the other way round & it's the ret that has a prob, just because the trv is on the cold pipe this means nothing, most modern trv's can be fitted on either end & alot of installers don't even check which is flow & ret before fitting them.
Back to top
 Alert Moderators
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Mon Oct 22, 2012 10:33 pm Reply with quote

CBF wrote:
how do you know that the flow is cold & the ret hot ? i would say it's the other way round & it's the ret that has a prob, just because the trv is on the cold pipe this means nothing, most modern trv's can be fitted on either end & alot of installers don't even check which is flow & ret before fitting them.


Good point, it could very well be the return, not sure why I assumed it was the flow. It's definitely the one with the TRV that is blocked.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52146
Location: London,
United Kingdom
Thanked: 3251 times

PostPosted: Tue Oct 23, 2012 12:08 am Reply with quote

Of course the hot one is always the flow.

You need to do the bucket test with each pipe.

But if you do that through the valve then remember the inlet to the valve may be blocked rather than the pipework.

DS40 will dissolve any oxide blockage but may be overwelmed by sludge in your system.

Tony
Back to top
 Alert Moderators
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Tue Oct 23, 2012 7:07 am Reply with quote

Agile wrote:
Of course the hot one is always the flow.

You need to do the bucket test with each pipe.

But if you do that through the valve then remember the inlet to the valve may be blocked rather than the pipework.

DS40 will dissolve any oxide blockage but may be overwelmed by sludge in your system.

Tony


Thanks Tony, I did the bucket test on both pipes and the lockshield side was flowing fine but the TRV barely dribbled. I did remove the TRV and all was well with it.

If I were to drain the system and inject DS40 into the blocked legs, would that be a safe and effective way of doing it?
Back to top
 Alert Moderators
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Fri Nov 02, 2012 10:48 pm Reply with quote

I've tried putting DS40 in the pipes and adding a small amount of pressure but it didn't work (made things slightly worse if anything).

The flow pipes are still blocked to 5 upstairs radiators. I've checked the pipes and it is the ones that get hot first that are blocked.

Is there anything else I can try?

I'm more than happy to get a pro in but the last 3 have failed (1 powerfushed to no avail, one said it was normal as the top of the radiators were hot at the time and the other said it just needs balancing).

I guess the most extreme option would be to take the floorboards up (T&G chipboard and under partion walls in places) and replace with 15mm. Would the system work with 15mm upstairs and 10mm downstairs?

Thanks in advance.
Back to top
 Alert Moderators
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3326
Location: Humberside,
United Kingdom
Thanked: 500 times

PostPosted: Fri Nov 02, 2012 11:18 pm Reply with quote

hm.


Connect the pipes up to a mains hose and flush through.
Powerflushing is over rated. You need some pressure behind it. icon_smile.gif
Failing that compressed air at 60 or 70 psi should do it. icon_smile.gif
Back to top
 Alert Moderators
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Fri Nov 02, 2012 11:36 pm Reply with quote

dcawkwell wrote:
hm.


Connect the pipes up to a mains hose and flush through.
Powerflushing is over rated. You need some pressure behind it. icon_smile.gif
Failing that compressed air at 60 or 70 psi should do it. icon_smile.gif


Cheers for that, I have tried using mains water without success with an elaborate device cobbled together with some copper pipe and a pressure meter to make sure I was getting plenty of pressure.

I've not tried compressed air, can I do that with a foot pump or would I need to get a compressor?
Back to top
 Alert Moderators
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3326
Location: Humberside,
United Kingdom
Thanked: 500 times

PostPosted: Fri Nov 02, 2012 11:39 pm Reply with quote

StvPL wrote:
dcawkwell wrote:
hm.


Connect the pipes up to a mains hose and flush through.
Powerflushing is over rated. You need some pressure behind it. icon_smile.gif
Failing that compressed air at 60 or 70 psi should do it. icon_smile.gif


Cheers for that, I have tried using mains water without success with an elaborate device cobbled together with some copper pipe and a pressure meter to make sure I was getting plenty of pressure.

I've not tried compressed air, can I do that with a foot pump or would I need to get a compressor?


Compressor need lots of it.
But if you did that with water you have a problem and a complete block.
Re-pipe. Probably a bent/crushed pipe.
Back to top
The following user says thank you to dcawkwell for this useful post:
StvPL (7 Nov 2012)
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52146
Location: London,
United Kingdom
Thanked: 3251 times

PostPosted: Fri Nov 02, 2012 11:54 pm Reply with quote

There is a way to put in more pressure and thats with a pressure washer pump. They can be up to 3000 psi.

Better to put together a tee piece with bleed off to regulate the pressure.

3000 psi would probably open a flattened copper pipe!
Back to top
The following user says thank you to Agile for this useful post:
StvPL (7 Nov 2012)
 Alert Moderators
SandyLyon

from United Kingdom

Joined: 21 Oct 2012
Posts: 230
Location: Lancashire,
United Kingdom
Thanked: 46 times

PostPosted: Sat Nov 03, 2012 9:48 am Reply with quote

Take great care if pressurising the system, make sure any other components on the installation can withstand the pressure (valves, pump, boiler etc).

Most pressure tests are done at 1st fix stage (just the pipe work, before anything else is connected). Typically on plastic the recommended pressure test is 1.5 times the max working pressure. However if there are any of the "older style" O ring first fittings a further test of 18 bar should be done.

As above, make sure all other components are ok at these pressures.

And remember, the pressure test is designed to test system soundness, and find any leaks or poorly made joints (could cause a fitting to "blow off")
Back to top
The following user says thank you to SandyLyon for this useful post:
StvPL (7 Nov 2012)
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36195
Location: Hampshire,
United Kingdom
Thanked: 1285 times

PostPosted: Sat Nov 03, 2012 10:19 am Reply with quote

if there is any flow at all, then a chemical can still get to the sediment. Once it is completely blocked chemicals will not travel through the pipe.

As an amateur, I have seldom used acid cleaners, as most of the sediment is black iron oxide that can be loosened with a simple non-aggressive cleaner. However I would recommend also fitting a systen filter to trap the loosened sediment before it has the chance to accumulate into a new blockage, even though you are going to drain it out at the end of the cleaning cycle. It will continue to trap circulating particles indefinitely. If you have done that and you still have a sediment blockage, the more aggressive acid cleaners can be used for a very short period.
Back to top
The following user says thank you to JohnD for this useful post:
StvPL (7 Nov 2012)
 Alert Moderators
StvPL

from United Kingdom

Joined: 17 Sep 2009
Posts: 11
Location: United Kingdom

PostPosted: Wed Nov 07, 2012 9:49 pm Reply with quote

Sorry for the delay but have had PC issues.

Thanks for all the suggestions, I have tried both non-acidic (X800) and acidic (DS40) without success. I do have a Magnaclean fitted so hopefully if I ever do resolve the problem it will stay solved.

I have had thermal imaging done to have a look at the pipe runs and it looks like the cold spots start at a right angle bend about 2 foot away from each of the cold radiators. Hopefully there will be a 15mm pipe reducing to 10mm along with an elbow there and hopefully this will be the source of the blockage.

Tomorrow one of the floorboards comes up to investigate.

If that doesn't work it will be back to the compressor.
Back to top
 Alert Moderators
leakydave

from United Kingdom

Joined: 02 Nov 2005
Posts: 604
Location: Gloucestershire,
United Kingdom
Thanked: 41 times

PostPosted: Wed Nov 07, 2012 10:05 pm Reply with quote

I have solved this sort of problem with my Rothenburger Test Bucket. Pressure water against the block and released. I have only tried this in an open vented system, not a sealed one.
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Wed Nov 07, 2012 11:25 pm Reply with quote

put some X400 in the system & leave it in there & run the heating normally until it's sorted it then flush it out, they do say you can leave it in there indefinatly but recommend upto 4 wks

http://www.sentinel-solutions.net/uploadedFiles/wwwsentinel-solutionsnet/resources_uk/NEW_product_fact_sheets/Product%20Facts%20X400%20System%20Restorer.pdf
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
How can I unblock microbore pipes? 5 200 Thu May 30, 2013 11:51 am
Using a pressure washer to unblock 40mm drain 7 160 Sun Mar 10, 2013 12:29 pm
Unblock a pipe plugged with silicone sealant? 11 700 Sun Mar 14, 2010 2:52 pm
Help me unblock my drain please 2 560 Sat Jun 26, 2004 3:16 pm
How to unblock a cold water pipe after mains tap ? 2 60 Sat Dec 07, 2013 7:04 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.