Judder / water hammer with an unvented HW cylinder

MJN

Joined
30 Apr 2008
Messages
781
Reaction score
122
Location
Wiltshire
Country
United Kingdom
We've recently moved into a new(ish) house with a Range Tribune unvented HW cylinder and are suffering (being annoyed by) juddering / water hammer and would be grateful for some advice as to how to eliminate it if possible.

Some observations which may or may not be relevant:

1. The noise appears to be coming from the pressure reducing valve (and not loose pipework etc) fitted adjacent to the cylinder.
2. The expansion vessel pressure is 3 bar (measured with the incoming mains off and a some taps open) as per the manufacturers installation instructions.
3. The incoming water pressure is 2 bar (measured before and after the PRV).
4. The PRV setting is unknown.
5. The noise is a single thud from the PRV when a tap is opened and, more evidently, when it is closed. The cold water taps appear to cause a louder noise than the hot. Even the kitchen, connected straight off the incoming mains (i.e. upstream of the PRV) causes a thud.
5. The shower, particularly when first used in the morning, causes repeated thuds for half and second or so if turned on quickly.

Does any of the above point to anything in particular? Are there other details I've missed out that could be pertinent?

Grateful for any pointers,

Mathew
 
Sponsored Links
Could be the PRV. As it's an unvented system, you need to get a G3-registered engineer in to have a look at it
 
Thanks Muggles - much appreciated.

As a point of general principle, do you think the expansion vessel being charged to 3 bar (i.e. higher than the 2 bar supply) could mean that it may not absorb transient pressure variations as well as if it were lower?

Thanks again,

Mathew
 
Sponsored Links
As a follow-up to this issue in case it's of use to anyone else but I have now lowered the EV pre-charge pressure to 2 bar (to match the incoming mains) and can confirm that the water hammer is no more.

Cheers,

Mathew
 