Maximum number of radiators


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
DLaing

from United Kingdom

Joined: 14 Jul 2004
Posts: 57
Location: United Kingdom

PostPosted: Sat Sep 24, 2011 10:18 pm Reply with quote

I've got a modern condenser boiler and a house with 4 floors. I've just added two radiators in the cellar meaning there are a total of 8 radiators on the ground floor and in the cellar.

I can get them to work individually or in pairs but not all together. The radiators on the top two floors are all fine.

The cellar and ground floor all work off the same 22mm pipe, with 4 T-d off the 22mm pipe and the other 4 t'd off 15mm at the end of the run.

Is there any way to make this work with this number of radiators? Before I added the two extra, everything worked perfectly.

Cheers,

David
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
jonjb

from United Kingdom

Joined: 19 Nov 2007
Posts: 535
Location: Birmingham,
United Kingdom
Thanked: 18 times

PostPosted: Sat Sep 24, 2011 10:46 pm Reply with quote

Firstly check that the kW output of your boiler is suitable for the total amount of radiators (and sizes) that you have.

Secondly you may may need to correctly balance the system. Click HERE for details.
Back to top
 Alert Moderators
DeltaT2

from United Kingdom

Joined: 24 Aug 2011
Posts: 1401
Location: Glasgow,
United Kingdom
Thanked: 165 times

PostPosted: Sun Sep 25, 2011 8:01 am Reply with quote

............4 Floors.........a wee clue there!!!
Back to top
 Alert Moderators
DLaing

from United Kingdom

Joined: 14 Jul 2004
Posts: 57
Location: United Kingdom

PostPosted: Sun Sep 25, 2011 8:53 am Reply with quote

Sitting here sweating like a pig! Rebalancing worked a treat for all bar the furthest away rad. Hopefully it will settle down but if it doesn't - any ideas?
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 51921
Location: London,
United Kingdom
Thanked: 3224 times

PostPosted: Sun Sep 25, 2011 9:00 am Reply with quote

It just needs balancing properly.

Oddly you did not mention your boiler model although thats irrelevant.

If the house is not zoned you need to balance ALL the rads! Its time consuming but not difficult. See the FAQ.

Tony


Last edited by Agile on Sun Sep 25, 2011 9:01 am, edited 1 time in total
Back to top
 Alert Moderators
DeltaT2

from United Kingdom

Joined: 24 Aug 2011
Posts: 1401
Location: Glasgow,
United Kingdom
Thanked: 165 times

PostPosted: Sun Sep 25, 2011 9:01 am Reply with quote

What's your circulation pump set at, have you got a 4 story house??
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8455
Location: Sussex,
United Kingdom
Thanked: 969 times

PostPosted: Sun Sep 25, 2011 10:17 am Reply with quote

Agile wrote:
It just needs balancing properly.

See How to balance a CH system.
Back to top
 Alert Moderators
DLaing

from United Kingdom

Joined: 14 Jul 2004
Posts: 57
Location: United Kingdom

PostPosted: Sun Sep 25, 2011 10:44 am Reply with quote

The boiler's an Ideal Logic combi 30 and I've got a dual pump system with under floor heating on the top floor. Everything is baking hot except for the one new radiator in the cellar.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8455
Location: Sussex,
United Kingdom
Thanked: 969 times

PostPosted: Sun Sep 25, 2011 11:17 am Reply with quote

DLaing wrote:
Everything is baking hot except for the one new radiator in the cellar.

Does the reluctant radiator get hot if you shut off all other rads and the underfloor? If so, then you still have a balancing problem.
Back to top
 Alert Moderators
The831Bunny

from United Kingdom

Joined: 18 Mar 2008
Posts: 870
Location: United Kingdom
Thanked: 423 times

PostPosted: Sun Sep 25, 2011 11:44 am Reply with quote

DLaing wrote:
The boiler's an Ideal Logic combi 30 and I've got a dual pump system with under floor heating on the top floor. Everything is baking hot except for the one new radiator in the cellar.


Check the new lock-shield valve is not screwed shut (they are sometimes like this out of the packet). Also an air lock may be stopping the circulation, as mention above, turn all rads off and leave problem cellar one on.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
noise when trv at maximum 13 140 Fri Dec 09, 2011 9:52 am
Maximum length of toilet waste pipe? 7 2080 Thu Jun 17, 2010 8:20 pm
maximum heat output per m2 from underfloor heating 24 7280 Mon Feb 15, 2010 4:06 pm
Maximum Boiler Pressure 3 400 Mon Dec 28, 2009 1:22 pm
maximum pressure drop on old pipework 17 460 Wed Dec 21, 2011 9:44 pm


 