Pressure at Zero, Worcester Greenstar 30cdi


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Wed Jan 30, 2013 9:31 pm Reply with quote

So, I have a towel rail which is cold at the top and hot at the bottom. I thought that I would follow internet instructions and bleed it. This however, has drained the pressure from the system. So, I went to increase the pressure and the turnkey which should be in the tray underneath is nowhere to be found.

I am pretty sure that this is an unvented system - we have a megaflow, if that has anything to do with it.

My question is this - am I going to do any damage to my system by still running the heating and hot water?

Also, the bleed valve was positioned upside down on the rail (helpful design, I know). I hope but am not certain that it is completely shut. Would I know if it was not?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
petertheplumber12

from United Kingdom

Joined: 05 Dec 2012
Posts: 695
Location: Surrey,
United Kingdom
Thanked: 96 times

PostPosted: Wed Jan 30, 2013 10:33 pm Reply with quote

You can go to their web site and ask for another key but if boiler is not loosing any more pressure then the rad valve is not leaking. Also if the boiler is still working then the actual pressure is ok. The boiler will stop working when pressure is too low. Or you may be able to get a key at your local boiler spares shop.
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Thu Jan 31, 2013 12:23 am Reply with quote

petertheplumber12 wrote:
You can go to their web site and ask for another key but if boiler is not loosing any more pressure then the rad valve is not leaking. Also if the boiler is still working then the actual pressure is ok. The boiler will stop working when pressure is too low. Or you may be able to get a key at your local boiler spares shop.


sorry pete but you aren't correct, the rad valve may still have a leak on it the OP has already said the boiler pressure is at zero, some WB will still run with no pressure & could mean the heat exchanger running dry which will certainly knacker it, you can get replacement keys at alot of plumbing merchants & i wouldn't run the boiler until you have increased the pressure,

OP what do you mean the bleed valve is upside down ?
Back to top
 Alert Moderators
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Thu Jan 31, 2013 10:50 pm Reply with quote

by upside down, i mean that it is positioned on the underneath bit of the rad.
so the screw that i opened up on the bleed valve is literally straight up.
Back to top
 Alert Moderators
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Thu Jan 31, 2013 11:03 pm Reply with quote

what im trying to understand though is whether, as an unvented system, it should definitely have a key, or whether i should be turning a valve to get the pressure up.
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Thu Jan 31, 2013 11:04 pm Reply with quote

i'm still having trouble seeing what you mean by upside down, the bleed nipple should be on the top & look something like the pic below or have a small bolt at the top at the back


Back to top
 Alert Moderators
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Thu Jan 31, 2013 11:13 pm Reply with quote

yes that is what it looks like. its just positioned in a way which means that the screw head (nipple?) is at the bottom, which meant that its worried me that i didnt get it back on right.

in the meantime, i have ordered a worcester key from the web, im just concerned about whether its actually the right thing that i am doing. i did leave the boiler on today but will switch the heating off and only use it for hot water (hopefully will prevent some damage).

i have tried looking up shops which sell the key but not having much luck so far. i live in n london, if anyone has any clues that would be really helpful too.
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Thu Jan 31, 2013 11:16 pm Reply with quote

no your boiler doesn't have a fill key as part of the boiler, what you should have is a filling loop, this will be two valves with a metal braded hose linking them, this will either be under the boiler or it could be in the airing cupboard with the megaflow it should have a pressure gauge to show the pressure it needs to be around 1 bar
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Thu Jan 31, 2013 11:21 pm Reply with quote

if that bleed nipple is at the bottom of the towel rail then you are never going to be able to bleed it as it should be at the top, if it is in the bottom connection then how are the rad valves connected as they need to go into the bottom connections
Back to top
 Alert Moderators
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Thu Jan 31, 2013 11:24 pm Reply with quote

CBF wrote:
no your boiler doesn't have a fill key as part of the boiler, what you should have is a filling loop, this will be two valves with a metal braded hose linking them, this will either be under the boiler or it could be in the airing cupboard with the megaflow it should have a pressure gauge to show the pressure it needs to be around 1 bar


aha!!
thank you

i am going to try this and see if i can get it working. will report back
Back to top
 Alert Moderators
asperity

from United Kingdom

Joined: 30 Jan 2013
Posts: 8
Location: United Kingdom

PostPosted: Thu Jan 31, 2013 11:31 pm Reply with quote

CBF wrote:
if that bleed nipple is at the bottom of the towel rail then you are never going to be able to bleed it as it should be at the top, if it is in the bottom connection then how are the rad valves connected as they need to go into the bottom connections


i am going to contact the manufacturer (Aeon) about the bleed nipple in the morning. It does seem weird.

BUT

in the meantime, i turned the handles on the valves, and the pressure has gone back up to 1 on the boiler. I couldnt actually see a pressure valve on the megaflow, but there are a lot of pipes in there.

thank you very much - you can send me your invoice anytime!!
Back to top
 Alert Moderators
CBF

from United Kingdom

Joined: 14 Oct 2012
Posts: 2164
Location: Hampshire,
United Kingdom
Thanked: 362 times

PostPosted: Thu Jan 31, 2013 11:41 pm Reply with quote

no probs glad you have it back upto pressure & you haven't knackered your boiler, coffee & two for me icon_smile.gif
Back to top
The following user says thank you to CBF for this useful post:
asperity (2 Feb 2013)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Pressure and flow issue with Worcester Greenstar 30CDi 3 1580 Fri Dec 31, 2010 3:14 pm
Worcester Greenstar 30CDI-pressure issue 19 10160 Mon Dec 14, 2009 7:23 pm
Worcester bosch Greenstar 30CDi 22 12100 Fri Mar 16, 2007 10:05 pm
Worcester Greenstar 30CDI: Awful groaning sounds 3 580 Sat Apr 24, 2010 9:03 pm
worcester bosch greenstar 30cdi gurgling when on water only 2 320 Fri Sep 03, 2010 6:12 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.