Pump runs continuously

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Sun Jan 08, 2012 7:03 pm Reply with quote

Hi There, this is my first post and am hoping to find the answer to my problem, i have a pump next to my storage tank that will not stop running. I think the pump is for circulating the water around the central heating circuit and the hot water circuit. yesterday morning we used the boiler to top up our hot water which i used the 1 hour boost on the time controller. we got the hot water ok but noticed 7 hours later the pump was still running. The only way i can stop it is to isolate the power supply next to the time clock and hw and ch controller. there is also a thermostat on the side of my storage tank which is a megaflow cl210 on what i think is a sealed unvented system. there are also 2 x 2 port valves on this system and a room thermostat. could anyone help me to locate the reason? we think this may have happened some time ago as well but today after switching the power back on the problem seems to have self rectified for now!! any advice much appreciated, thanks.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Lower

from United Kingdom

Joined: 22 Dec 2005
Posts: 527
Location: Leicestershire,
United Kingdom
Thanked: 24 times

PostPosted: Sun Jan 08, 2012 7:11 pm Reply with quote

What is the make and model of the boiler?
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Sun Jan 08, 2012 7:12 pm Reply with quote

hi there, its a warmflow 120/150
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 10:46 am Reply with quote

Is my problem likely to be caused bye one of the valves or could it be a boiler problem?
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52963
Location: London,
United Kingdom
Thanked: 3340 times

PostPosted: Mon Jan 09, 2012 10:56 am Reply with quote

I am guessing that this is a hot water circulation bronze pump.

Sometimes these are fitted ( badly ) to run all the time.

In better installations they are on a thermostat and/or a timeclock.

It would be better for you if you had a heating engineer inspect it and tell you exactly what it does and how it is or should be controlled and make any improvements or repairs as necessary.

I suspect that the pump is correctly fitted with appropriate controls but you are ( wrongly ) not fully heating your cylinder. You should have the hot water selected on for most of the day! NOT to just heat it for a short period every now and then.

Tony


Last edited by Agile on Mon Jan 09, 2012 11:09 am, edited 1 time in total
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 11:06 am Reply with quote

But it has never ran permanently before!
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52963
Location: London,
United Kingdom
Thanked: 3340 times

PostPosted: Mon Jan 09, 2012 11:46 am Reply with quote

Its probably the first time that you have noticed it or not properly heated the whole cylinder as you should!

Tony
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 12:01 pm Reply with quote

Agile wrote:
Its probably the first time that you have noticed it or not properly heated the whole cylinder as you should!

Tony


We would Definately have noticed. We usually heat all our water on economy 7. Also the pump is now not running after the hour boost if we use it. It seems to be an intermittent fat and would like some assistance in finding the problem.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52963
Location: London,
United Kingdom
Thanked: 3340 times

PostPosted: Mon Jan 09, 2012 12:31 pm Reply with quote

keggy wrote:



We usually heat all our water on economy 7
. Also the pump is now not running after the hour boost if we use it. It seems to be an intermittent fat and would like some assistance in finding the problem.



Why do you do that?

I dont follow fuel prices very closely and with oil it depends so much on storage capacity and when its bought. But I would be very surprised if electricity is cheaper than heating with the boiler and particularly when the boiler is already being used for central heating.

Its possible that when the CH is not in use it would be cheaper to do the water heating with the economy 7 as the boiler is less efficient on part load.

I still suspect your pump IS correctly controlled and you have just had a situation where the water is not hot enough to make its stat turn it off. You can only check that by examining the system and measuring the temps. ( Or getting a heating engineer to do that, possibly when its next serviced. ).

Tony
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 12:51 pm Reply with quote

Agile wrote:
keggy wrote:



We don't use central heating very often. I use far to much oil when we do!!! My house had 3 wood burners which provide a good temperature as we get the
Wood free..night rate a kwh is 5p +vat. Oil alone to heat the water for our tank would be much higher from my workings..



We usually heat all our water on economy 7
. Also the pump is now not running after the hour boost if we use it. It seems to be an intermittent fat and would like some assistance in finding the problem.



Why do you do that?

I dont follow fuel prices very closely and with oil it depends so much on storage capacity and when its bought. But I would be very surprised if electricity is cheaper than heating with the boiler and particularly when the boiler is already being used for central heating.

Its possible that when the CH is not in use it would be cheaper to do the water heating with the economy 7 as the boiler is less efficient on part load.

I still suspect your pump IS correctly controlled and you have just had a situation where the water is not hot enough to make its stat turn it off. You can only check that by examining the system and measuring the temps. ( Or getting a heating engineer to do that, possibly when its next serviced. ).

Tony
Back to top
 Alert Moderators
45yearsagasman

from United Kingdom

Joined: 14 Mar 2010
Posts: 4879
Location: Norfolk,
United Kingdom
Thanked: 823 times

PostPosted: Mon Jan 09, 2012 1:38 pm Reply with quote

I would suspect that one of your 2 port valves is the cause, in that the end switch is staying closed intermittently when the valve has closed off.
Did the boiler fire from time to time when the pump was running on?
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 1:47 pm Reply with quote

Yes, I think it may have fired up a couple of times but mostly just the pump running and a power light on on the boiler.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52963
Location: London,
United Kingdom
Thanked: 3340 times

PostPosted: Mon Jan 09, 2012 1:56 pm Reply with quote

At the moment we dont know if this is the one heating pump or its a hot water loop pump.

In the case of the latter then there would be another pump elsewhere for the heating water ( and that could be inside the boiler casing ).

Can you post a picture showing the pump and the pipes connecting it to the cylinder?

Tony
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 2:06 pm Reply with quote

I think there is only the one pump and 2 x 2 port valves. One valve is on the hot water loop on the bottom of the tank and the other controls the rads I think. I can post a picture when I get home later if that's ok.


Agile wrote:
At the moment we dont know if this is the one heating pfump or its a hot water loop pump.

In the case of the latter then there would be another pump elsewhere for the heating water ( and that could be inside the boiler casing ).

Can you post a picture showing the pump and the pipes connecting it to the cylinder?

Tony
Back to top
 Alert Moderators
keggy

from United Kingdom

Joined: 08 Jan 2012
Posts: 17
Location: Lincolnshire,
United Kingdom

PostPosted: Mon Jan 09, 2012 5:33 pm Reply with quote

Hello again, If I have done I correctly there should be some photos of my pump and valves now on this post..It was hard to fit everything into the frame so if there's any more info you require other than this I will try to explain it. I think the valve you can see is for the central heating which we rarely use and the other valve is just out of sight on the bottom of the storage tank on the primary flow port of the tank.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Boiler pump runs continuously - what is wrong? 15 3260 Mon Mar 21, 2011 4:54 pm
Pump Runs Continuously 2 2620 Tue Dec 26, 2006 11:31 am
Gledhill Boilermate 2 Pump Runs Continuously 11 360 Mon May 27, 2013 2:37 pm
Pump runs continuously (no CH/HW call; boiler switched off) 16 8580 Thu Feb 19, 2009 3:59 pm
Central Heating Pump Runs Continuously 8 1620 Sat Jan 23, 2010 3:44 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.