Vaillant TURBOmax VUW 282 - DHW demand problem

Joined
4 Mar 2012
Messages
8
Reaction score
0
Location
Sussex
Country
United Kingdom
Had a similar problem on this boiler before, where the divertor valve was replaced (just a few years back). The only problem then was the switch lever had broken. I have recently discovered this lever can be bought as a separate item.

My suspicions this time is:
1. The switch lever has again broken.
2. The diaphragm has gone.

Note: the micro switch is fine, the lever is moving very slightly when HW is demanded but is not engaging with the micro switch.

Can anyone tell me if the switch lever can be removed/replaced with the diverter in situ, if i can avoid it I really don't want to be taking the diverter out.

If this is possible can you explain the procedure, I have already removed the micro switch to get closer but I can't see how to remove the lever and I really don't want to break it if it is fine.

Thanks in advance...
 
Sponsored Links
Thanks for your response,

I have replaced the whole diverter valve recently, not just the lever.
If I need to remove the whole diverter first to replace the switch lever then I will check the diaphragm first. Many thanks.
 